    Greg05's Avatar
    Greg05 Posts: 2, Reputation: 1
    New Member
     
    #1

    Sep 3, 2007, 03:41 PM
    Rudd System
    I have a brand new Rudd central air system. Worked great for the first month and a half. Now the condensing unit will cycle on and off in 20-30 second intervals. I checked the breaker and all connections. Is there maybe a high pressure switch that I may be missing?
    CaptainRich's Avatar
    CaptainRich Posts: 4,492, Reputation: 537
    Cars & Trucks Expert
     
    #2

    Sep 3, 2007, 03:57 PM
    Quote Originally Posted by Greg05
    I have a brand new Rudd central air system. Worked great for the first month and a half. Now the condensing unit will cycle on and off in 20-30 second intervals. I checked the breaker and all connections. Is there maybe a high pressure switch that I may be missing?
    There may be a leak at one of the connections.
    You're probably under warranty, so I'd not mess with it for fear of voiding that warranty.
    Any toll free number on your receipts?
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #3

    Sep 3, 2007, 04:00 PM
    Like CaptainRich mentioned it would be under wwarranty. Call the installer back for service
    Greg05's Avatar
    Greg05 Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 3, 2007, 04:09 PM
    Job was done a last second side job by my friend (fully licensed hvac tech / contractor) before he moved to the islands. So not worried about any warranty but the MFG. Will check pressures to see if there is a leak. Any cance it could be a bad t-stat?
    CaptainRich's Avatar
    CaptainRich Posts: 4,492, Reputation: 537
    Cars & Trucks Expert
     
    #5

    Sep 3, 2007, 04:14 PM
    Quote Originally Posted by Greg05
    Job was done a a last second side job by my friend (fully licensed hvac tech / contractor) before he moved to the islands. So not worried about any warranty but the MFG. Will check pressures to see if there is a leak. Any cance it could be a bad t-stat?
    A faulty t-stat could cause that, I guess, but I wouldn't think it to be so responsive.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    Sep 3, 2007, 06:26 PM
    Easy to check stat, just disconnect it and connect the red wire to the yellow and green. The system should run until you disconnect them.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Sep 4, 2007, 04:12 AM
    Outdoor unit may be equipped with a low vapor pressure switch connected to a compressor recycle time delay. If system has leaked down refrigerant, it will run briefly until vapor switch opens. Compressor stops, pressure climbs back up to reset switch, & time delay restarts unit after about 5 minutes. Repeats. Sound familiar? Check for oily residue where refrigerant lines connect to units.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

RUDD 10 SEER AC fan working intermittently [ 2 Answers ]

I have a RUUD 10 SEER AC outside unit. The AC repairman put in a capacitator temporarily so that the unit would still work that had more OHM. I asked about this because I was concerned that this could cause damage. He assured me that it would not as the original capacitator was not available and...

Changing from a Rudd to a Hunter thermostAT [ 1 Answers ]

I bought a hunter 44360 digital thermostat to replace a Rudd. The Rudd was wired Y-Yellow, G-green, E-White, R- Red, B-Blue, and a brown on X. The Hunter has G, RC, RH, Y/O, W/B and Y1. I can't seem to get the outside fan to run. Also before changing the thermostat, the blower fan constantly...

Changing from a Rudd to a Hunter thermostAT [ 2 Answers ]

I bought a hunter 44360 digital thermostat to replace a Rudd. The Rudd was wired Y-Yellow, G-green, E-White, R- Red, B-Blue, and a brown on X. The Hunter has G, RC, RH, Y/O, W/B and Y1. I can't seem to get the outside fan to run. Also before changing the thermostat, the blower fan constantly...

Changing from Rudd to Honeywell Thermostat [ 2 Answers ]

I am trying to change from a Rudd thermostat and system to a Honeywell RTH 7500 Thermostat. Having problems with the wiring as it does not work properly. The system that I have is a heat pump in the attic with auxiliary heat and an air conditioning system outside. I am not sure if this should be...

How do I increase H2O pressure on well system with a water filtration system? [ 2 Answers ]

Howdy, I would like to know how I can increase my water pressure. My current system uses a well pump with a small pressure tank, and "D" control valve. It then runs through a WATERSOFT filtration tank, RAINSOFT water softner, and on the Hot water side, an AQUASTAR on demand hot water system. I...


View more questions Search