    400 ft. cable run
    I have wired an exterior garage with some very basic electrical. I have 6 outlets (for convenience, only one or two would be used at once), Three 75 watt lights and an exterior spotlight.

    The garage is about 400 feet from the breaker panel. What size wire would this require (wire will be buried) and is 400 feet too long?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 30, 2007, 03:55 PM
    Assuming a full 20 amp load for one circuit, # 4 copper will give about 5 volts dropped, the max is 5% of 120+6 max Vd.

    #2 aluminum will give 5.1 Vd, so is a good substitute, if allowed in your area.

    Would be the same for two circuits.

    Use XHHW insulation if the entire run is conduit, or use USE or URD cable if direct burial. Even use 4" DB duct if direct burial cable is used, works good as extra protection, and allows upgrades.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wall mount for cable, how do I prepare for cable line? [ 3 Answers ]

I want to move my T.V. across the room, I have a wall mount with the wire there. What do I do to the wire that is not cable prepared to look like the one that is now being used? I need step by step instructions. If anyone can help me please!! :confused: Signed single mom trying to save a few...

Do I need conduit to run a 220v cable through my cellar? [ 10 Answers ]

I'm running a 2-2/4 aluminum cable for a 220v circuit from my barn from the panel in my house. Once entering the home (from the 36" deep in-conduit run from the barn), I have to string the cable through the mechanical area (cellar) of the house, then through a center-home crawl space and then...

400 digit number [ 1 Answers ]

2 numbers if multipied would generate a 400 digit number?

Can I run 400 amps with two 200 amp boxes? [ 6 Answers ]

I want to run 400 amp service in my new home and I was wondering if it is possible to run two separate 200 amp boxes instead of 1 400 amp with is much more expensive. If so do I need a main 400 amp lug or can I use the two separate 200 amp mains?


View more questions Search