    Going from nongrounded to grounded
    I'm a handyman and curious is there a easy way to change a non grounded outlet into a grounded outlet
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jul 29, 2007, 07:37 PM
    You would need 3 conductors(Hot, Neutral, and ground), See if you can pull new wiring through attic? Or underneath?
    I never deal with it, when I did, I replaced it. Don't know of some exception that allows neutral and ground tied together? Hopefully TK will see this post, and shed some light. I'm curious also. He probably has it in his head.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jul 30, 2007, 02:38 AM
    There is no exception to connect neutrals and grounds for an outlet. As Strat sates,you can run new cable with a ground wire. Or you can use a GFI breaker or outlet, change any 2 wire outlets to 3 wire that will be protected by the GFI, and apply the "No Equipment Ground" label that comes with the GFI outlets.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Should siding be grounded? If yes, how? [ 4 Answers ]

Hi all, great site. I am a new member and I have three questions about grounding. 1. I have installed a copper grounding rod which I intend to use to ground a portable generator. It is an 8ft rod with the shielded #12 grounding wire. I managed to get six feet into the ground which is very...

Should the light switch be grounded? [ 3 Answers ]

I am doing some wiring as part of finishing my basement. Is it required to ground the switches? Most of the regular two way switches have ground screw built in. Thanks

Grounded delata power system [ 5 Answers ]

hi guys, anybody who can explain me the grouded delata power system? I have seen one installation in ksa wherein a delta seconondary of a three phase transformer wherein one of the phase leads is connected to ground. the voltage reading is as ff. phase A to Grnd = 230 phase B to Grnd = 230...

Problem with grounded neutral. [ 1 Answers ]

I have an exterior GFCI receptacle that failed. I bought a new GFCI to replace this one. When I opened the outlet box, I discovered that the ground was tied both to the ground screw on the receptacle as well as the neutral plate. I thought I would correct this with the new GFCI receptacle, but...

Outlets(receptacles) not grounded... what to do? [ 4 Answers ]

I embarked on a project to replace all the 15amp duplex wall receptacles in my living room yesterday because I wanted white outlets instead of the black ones that were installed. So I turned off the power and started to swap them out. They are 15amp duplex, 125-volt u-grounded receptacles. Much to...


View more questions Search