    Cable size for 320 amp service , single phase
    I'm installing a 320 amp single phase service. What size cable do I need to use? I'll be using copper. Also what size for 200 amp?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 15, 2007, 03:52 AM
    Assuming this is a residential service, the 320 amp will be minimum #400 MCM Copper with either THHN/THWN or XHHW insulation, the 200 amp will be #2/0 with either of the same insulations.

    Assuming the 320 amp is the feeder to the meter, no equipment ground is needed. The grounding electrode conductor will be # 2 copper. The 200 amp is probably for the panelboards, and each feeder will need an equipment ground conductor of #6 copper. Be sure to separate, insulate and isolate the neutral from the equipment ground at each panel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between single phase and 3-phase motors [ 4 Answers ]

Difference between single phase and 3-phase motors

Wiring 220V Single Phase 30 AMP car lift motor [ 5 Answers ]

Recently I perchased 9000 pounds 2 post car lift, and only after car lift has arrived I've found out that the requirements for the motor are 220VAC Single Phase 30 AMP 60 Hz. Can somebody please explain how to use this motor safely with the standard power outlet. Thank you.

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

How am I going to size my 3 phase X'mer with 1 phase load using current as reference [ 3 Answers ]

Hi, I'm Peping: I have 90 pieces of single phase loads with current of 2 Amperes. This will be loaded to a 3 phase transformer, Wye connected having a line to line voltage of 220 Volts. What will be the size of the transformer required for the mentioned loads? Many thanks, Peping


View more questions Search