    One hot room
    Hi all. I just bought an older home. It had a new master bedroom added in the mid 90's. The original house stays cold, but the master doesn't get cold at all. I checked the planum?? In the attic, and the duct is attached and not leaking air. Because of the way the roof was installed over the addition, I can't follow the duct all the way to the vents. How would I check to see if the duct is pinched or obstructed? Any suggestions would be really helpful. I'm in Louisiana and it's hot and muggy even at night.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jun 25, 2007, 01:42 PM
    Sounds like this add-on room is drawing from the very end of the supply ducts. Many people add on a home and assume their furnace can handle the extra space only to be disappointed. This may be your case. If there ius a return in the bedroom make sure its open and partially close the returns in other parts of the house. Also try partially closing the supply registers in the lowest level to help boost the amount of air reaching the bedroom. You can also add a duct boost fan.
    msfixit1978's Avatar
    msfixit1978 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 25, 2007, 01:52 PM
    Thanks you for your answer. I only have one return in the house and that's in the door where the inside unit is. Do I need to install a return in the MB? The house is only 1492 hsqf. The duct that runs to the MB is probably the longest duct. Is it difficult to wire in a booster fan?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Jun 25, 2007, 01:57 PM
    Duct boostera aren't too difficult. The manufacturers know DIY folks will install so they give great instructions. Getting the 110 vac is usually the hard part.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air conditioning - hot room [ 2 Answers ]

I have one bedroom that is about 12 X 15 with 10 ft ceiling used by teenager who keeps door closed a lot. Gets hot at night vs rest of house. I have heard that a small return will be more beneficial than another supply duct. Note: Main return for house is is this room closet and draws from hall...

Feeling hot hot (water) and then it is not at all hot [ 3 Answers ]

We have scalding hot water for a couple of minutes and then it cuts off . We have a state water heater model e5650dols. We set our temperature lower and reset the unit only to have it replicate the same problem. Is this due to the theromostat if so is it the lower or the upper. How do you tell??...

Hot room above garage [ 2 Answers ]

My master bedroom is above our garage which gets very hot and has no insulation or ventilation. During the summer, the master bedroom is much warmer than the rest of the house. Looking for a solution. Should I have another duct installed or will venting the hot air out of garage via fan provide...

Radiators hot but hot water from taps luke warm [ 1 Answers ]

Hi, First of all I am novice.. a real novice when it comes to plumbing, so please be easy on me :) I hope someone can shed some light on this weird problem. I have a conventional boiler with a hot water tank in the bathroom and 2 tanks in the loft. The radiators in the house are fine, they...


View more questions Search