    Condenser tries to start occasionally
    I'm a tech w/certification but little field experience. I have central a/c condensing unit that hasn't been in use for 2 years. No refrigerant in system so I partially charged it. Replaced capacitor. Tested contactor and compressor terminals (got readings of about 1, 3, and 4) and both good. No burnt wires. Fan runs. Compressor NOT hot-only warm from sunshine. Out of 10 times of powering unit up, compressor has come on for maybe 20 seconds and shut down 3 times only. Has internal overload. Everything looks good. What now? It's an old Lennox unit without low pressure switch. None of my tech friends know what to do other than try new compressor.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jun 14, 2007, 06:19 AM
    Did you check compressor capacitor?
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #3

    Jun 14, 2007, 01:18 PM
    Did the compressor loose all of its oil? Have you tried a hard start kit? Is the amp draw of the compressor with in tolerances stated on the condenser label?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #4

    Jun 14, 2007, 08:55 PM
    What is the model number? Are you sure there are no pressure switches? Even some of the older lennox models had loss of charge switches. Does the contactor stay pulled in?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Condenser wiring [ 5 Answers ]

Hi, I am installing wiring for a new central air condenser that is being installed next week, and I wanted to make sure I was not missing anything. The HVAC installer told me that I needed #8 and 40 amps. I have a flexible whip to go from the disconnect to the condenser and have run (2) #8 wires...

Condenser Fan Wiring [ 2 Answers ]

I Purchased A New Condenser Fan. The Old Fan Had Three Wires One To The Contactor(black) Then Yellow Wire To The Capacitor And Brown Wire To Capacitor. The New Motor Has Four Wires Brown , Brown With White Strip, Black And Purple. The Fan Diagram Shows You Can Connect With Only Three Wires. It...

AC condenser not kicking on. [ 1 Answers ]

I live in SW Florida and yeasterday there was a power outage that left us without power for some time. FPL said that there was a main line that was tken down by a tree. We did not immediately turn the AC on after the power came back on (the thermostat was off when power returned). We turned it...

Condenser wiring [ 2 Answers ]

Hi, I am installing wiring for a new central air condenser that is being installed next week, and I wanted to make sure I was not missing anything. The HVAC installer told me that I needed #8 and 40 amps. I have a flexible whip to go from the disconnect to the condenser and have run (2) #8 wires...

Why no insulation in condenser unit ? [ 1 Answers ]

I'm curious why when A/C units are installed, why only the cold Line is insulated from the condenser unit to the evaporator. Why is the cold line not insulated on the inside of the condenser Unit?. seems like an energy waste. Questions: Is it OK to insulate the cold line inside the condenser...


View more questions Search