    Toilet Pipe Run
    Hello. I'm installing a toilet/lav/shower in my basement. My question is... Can I sit the toilet flange directly on top of a 4" 90 degree closet bend PVC fitting? This fitting has only one hub, which will connect to a 4" PVC at 1/4" per foot over 3.5 feet and tie into a cast iron tee fitting on the existing vertical soil pipe. I hoped to run a vertical pipe 6" out of the 90 degree PVC fitting to tie into the toilet flange, however, I do not have the clearance.

    I thank you in advance for your help.
    Flickit's Avatar
    Flickit Posts: 278, Reputation: 2
    Full Member
     
    #2

    Jun 7, 2005, 07:56 AM
    The closet bend...
    Quote Originally Posted by jk47
    Hello. I'm installing a toilet/lav/shower in my basement. My question is...Can I sit the toilet flange directly on top of a 4" 90 degree closet bend PVC fitting? This fitting has only one hub, which will connect to a 4" PVC at 1/4" per foot over 3.5 feet and tie into a cast iron tee fitting on the existing vertical soil pipe. I hoped to run a vertical pipe 6" out of the 90 degree PVC fitting to tie into the toilet flange, however, I do not have the clearance.

    I thank you in advance for your help.
    ... as the name implies is suited for this purpose. I wish I could have found one of these when I went shopping for one but instead got handed an ordinary 1/4 bend. Why not cut the 6" pipe to length if as you say you don't have enough clearance? BTW... the cast iron tee fitting should be a sanitary tee if you have other drains connecting upstream from this connection point.
    jk47's Avatar
    jk47 Posts: 6, Reputation: 1
    New Member
     
    #3

    Jun 7, 2005, 09:43 AM
    Neoprene Couplings
    If I were to cut the 6" pipe to length, I would have to cut it at the top of the 1/4 bend. Instead, I plan to cement a closet flange directly to the top of the 1/4 closet bend. After talking to a local plumber and reading your reply, this is commonly done. I did not realize this and I thank you both.

    Here is my new problem. I connected the cast iron (sanitary) tee the the existing 4" cast iron vertical soil pipe with Fernco Proflex Couplings (Neoprene rubber w/ stainless steel clamps). I cannot get a tight seal. Water drips from the coupling when the upstairs facilities are used. I tried tightening the clamps, but I can't stop the leak.

    Are there any tricks to using or installing these couplings? Has anyone had any experience with another brand? Thanks for any help.
    Flickit's Avatar
    Flickit Posts: 278, Reputation: 2
    Full Member
     
    #4

    Jun 7, 2005, 11:40 AM
    If you check some...
    Quote Originally Posted by jk47
    If I were to cut the 6" pipe to length, I would have to cut it at the top of the 1/4 bend. Instead, I plan to cement a closet flange directly to the top of the 1/4 closet bend. After talking to a local plumber and reading your reply, this is commonly done. I did not realize this and I thank you both.

    Here is my new problem. I connected the cast iron (sanitary) tee the the existing 4" cast iron vertical soil pipe with Fernco Proflex Couplings (Neoprene rubber w/ stainless steel clamps). I cannot get a tight seal. Water drips from the coupling when the upstairs facilities are used. I tried tightening the clamps, but I can't stop the leak.

    Are there any tricks to using or installing these couplings? Has anyone had any experience with another brand? Thanks for any help.
    ... posts/replies by Speedball1 I think you will find the best way to join cast to cast is with solder and what have you (not an expert with cast). Find one or more of these and you will see it is quite simple to do if you follow Tom's (Speedball1's) recommendations.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #5

    Jun 8, 2005, 03:39 PM
    Quote Originally Posted by jk47
    If I were to cut the 6" pipe to length, I would have to cut it at the top of the 1/4 bend. Instead, I plan to cement a closet flange directly to the top of the 1/4 closet bend. After talking to a local plumber and reading your reply, this is commonly done. I did not realize this and I thank you both.

    Here is my new problem. I connected the cast iron (sanitary) tee the the existing 4" cast iron vertical soil pipe with Fernco Proflex Couplings (Neoprene rubber w/ stainless steel clamps). I cannot get a tight seal. Water drips from the coupling when the upstairs facilities are used. I tried tightening the clamps, but I can't stop the leak.

    Are there any tricks to using or installing these couplings? Has anyone had any experience with another brand? Thanks for any help.


    Cast Iron can be lumpy and have irregular walls so that the clamp won't make a watertight seal. Try this. Take some silicon gel and coat the pipe under the coupling clamps and then tighten the clamps. Good luck, Tom
    jk47's Avatar
    jk47 Posts: 6, Reputation: 1
    New Member
     
    #6

    Jun 9, 2005, 06:28 AM
    Venting
    Thanks Tom. I bought a different type of coupling... these ones have 4 clamps and seems to be holding so far.

    I now have a question about venting. I understand that the toilet is self venting. My question is... for the shower and lav... if the 2" PVC drain lines discharge close enough to the existing 4" Cast Iron soil pipe (which vents through my roof), are they properly vented? Please see the attached picture.

    I thank you for your help.
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #7

    Jun 9, 2005, 10:17 AM
    "I understand that the toilet is self venting."
    Not exactly. In most applications the toilet is wetvented by the lavatory vent.
    I hate to break this to you but your diagram tells me nothing. All I see is two 2" pipes connecting to a 4" pipe. I assume the lavatory is vented and 4 feet is within code. However you give me no information about the 7 foot run of 2". If both 2" pipes are arrempting to vent out the 4" stack vent then you are discharging a major fixture past two unvented minor ones and that's way out of code. Suggestion: Vent the lavatory out the roof, tie the other 2" into the lav drain and the entire group will be vented. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Toilet drain pipe broken! [ 6 Answers ]

My husband removed a toilet today, it was leaking sewage on the floor and into the other room. When we pulled the toilet off, we knew why. The flange came with the toilet when we pulled it off along with some of the drain pipe. Clearly the pipe has been broken for some time. The flange was almost...

Extending pipe under toilet [ 2 Answers ]

I just recently moved into a townhouse and wanted to fix it up a little by installing laminate floors in my bathroom. I currently have linoleum on my floors and figured that once I replaced the linoleum with the laminate it may shorten the pipe underneath of my toilet. Is it possible for me to...

PVC pipe leak from toilet [ 3 Answers ]

Help.. My wife and I bought our first house 5 months ago. We are not used to living in a home with 2 floors and a basement. So, the toilet on the upper floor started leaking a few drops a minute, so it is not serious yet:). The drops are forming on the elbow joint of the PVC pipe in the...

Setting a toilet on a crooked pipe [ 5 Answers ]

I am about to install a toilet in my basment. But the PVC waste pipe coming up through the concrete and subfloor is not perfectly level... it is cocked just a bit. Its not coming out at a 45-degree angle or anything... just slightly off perpendicular. I imagine (hope) that once I cement the...

Bathroom sink wall pipe drain pipe [ 2 Answers ]

My house was built in early 70's.. No plastic.. I'm putting in a new sink and had to remove the wall pipe that goes into the wall.. I needed a longer one. It seem where it goes in behind the wall into the plumbing there was some type of gasket as pieces of it fell out when I removed the pipe.. I...


View more questions Search