    jensie's Avatar
    jensie Posts: 2, Reputation: 1
    New Member
     
    #1

    Nov 2, 2007, 08:16 PM
    Toilet Distance from Wall
    Hi,

    We are remodeling our bathroom and the toilet needed to be moved down about two feet along the same wall from its old location. The plumber has placed it so that the back of the toilet will not sit against the wall, but out from the wall, leaving a gap of about two inches between the wall and the back of the toilet. He told my husband that this is because NC building codes require that the center of the toilet flange be a minimum of 15 inches from a finished wall. Can this be true? I have never seen a residential toilet that did not sit flush back against the wall.

    Thanks for any help,
    Jen
    --------------------------------------------------------------------------------

    Hi tom,

    Thanks for replying to my question. Can you tell me more about the offset flange?

    Thanks again,
    Jennifer
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #2

    Nov 3, 2007, 04:29 AM
    Quote Originally Posted by jensie
    Hi,

    We are remodeling our bathroom and the toilet needed to be moved down about two feet along the same wall from its old location. The plumber has placed it so that the back of the toilet will not sit against the wall, but out from the wall, leaving a gap of about two inches between the wall and the back of the toilet. He told my husband that this is because NC building codes require that the center of the toilet flange be a minimum of 15 inches from a finished wall. Can this be true? I have never seen a residential toilet that did not sit flush back against the wall.

    Thanks for any help,
    Jen
    The fifteen inch clearance requirement is from side to side, not front to back -- 15" left and right of the centerline of the closet flange.

    Was there a framing member below the floor that prevented him from roughing it in the correct distance from the back wall (12-3/4" from the back wall to the centerline of the closet flange is typical) or is he just an idiot?

    All is not lost, though, TOTO sells a one piece WC that will accommodate a 15" rough-in. When ordering the toilet, you will need to specify a 15" rough-in floor flange, though.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Nov 3, 2007, 07:39 AM
    Growler gave you one option. However, Toto's a bit pricey. Let me give you a less expensive way to get that toilet back against the wall. They make offset closet flanges for just your situation. If you're interested click on back and I'll put up a link and a image. Regards, Tom
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Nov 3, 2007, 12:01 PM
    Hey Jen,

    Off set flanges,(see image) are used when a toilet has to be moved a short distance and moving the rough in is just too much hassle. They replace the flange that you now have and perform the same function. If you would like to see a selection I will have to know what material your drainage pipes are made of. As a rule offset flanges are used to correct mistakes. As with any plumbing installation the very best way is to do it right the first time.
    Have great week end, Tom,
    mike08201's Avatar
    mike08201 Posts: 32, Reputation: 1
    Junior Member
     
    #5

    Nov 4, 2007, 05:42 AM
    I delibrately set my flange 13" off the wall to generate a 1" gap between the tank and te wall. I can't stand it when they are tight (used a toilet that needs 12")

    To each their own
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #6

    Nov 4, 2007, 07:09 AM
    I'm assuming this is a personal preference for your own home, and that you aren't actively out there Plumbing outside of normal practices and conventions for paying customers, right?
    mike08201's Avatar
    mike08201 Posts: 32, Reputation: 1
    Junior Member
     
    #7

    Nov 4, 2007, 10:14 AM
    Quote Originally Posted by iamgrowler
    I'm assuming this is a personal preference for your own home, and that you aren't actively out there Plumbing outside of normal practices and conventions for paying customers, right?
    You are correct in your assumptions. 1" difference invokes that type of sarcastic response out of you. Interesting. You live up to your nick.
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #8

    Nov 4, 2007, 10:27 AM
    Quote Originally Posted by mike08201
    you are correct in your assumptions. 1" difference invokes that type of sarcastic response out of you. Interesting. You live up to your nick.
    No sarcasm intended.

    It was something that came up recently with a new employee and an angry homeowner.

    Fortunately it was caught before the floor was tiled and we were able to correct it.

    More than anything else, I was just trying to gauge how commonplace the practice was, that's all.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #9

    Nov 4, 2007, 10:32 AM
    Quote Originally Posted by mike08201
    I delibrately set my flange 13" off the wall to generate a 1" gap between the tank and te wall. I can't stand it when they are tight (used a toilet that needs 12")to each their own
    Ahh! But growler has a point. There's a reason for the 12 inch rough in. We leave just a tad of give in a tank when bwe install it. This allows the tank to give a bit when you lean back on it. If the tank couldn't give and was tight against the bowl it would put a strain on the tank bolts and crack the tank. The wall will stop the tank before it can move back enough to put a strain on the tank bolts. Having too much play behind the tank would allow the tank to tilt back far enough to break the bolts right out of the china tank. Now this may never happen, but it could and that's why we take steps,( the 12" rough) to see that it don't. Hey! I've shown you mine, now you show me yours. What's your reason for keeping it away from the safety of the wall? And don't mind growler. He's a top grade mechanic but like all canines his bark is worse then his bite. Regards, Tom
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #10

    Nov 4, 2007, 10:37 AM
    Quote Originally Posted by speedball1
    . . . .but like all canines his bark is worse then his bite.
    >hisses and spits<

    That's 'feline' to you, Bub.:D
    jensie's Avatar
    jensie Posts: 2, Reputation: 1
    New Member
     
    #11

    Nov 6, 2007, 09:23 PM
    Quote Originally Posted by iamgrowler
    I'm assuming this is a personal preference for your own home, and that you aren't actively out there Plumbing outside of normal practices and conventions for paying customers, right?
    Just to give an insight into this - when my husband called the plumbing company the day after this happened, the second guy who had been working on our job actually said that it's up to the customer - some prefer the tank one inch from the wall, some two inches.. . Oh, puh-lease. What a bunch of baloney. There was no mention of codes this time, just a whole load of CYA.

    As I page through this lovely book on bathroom design I am holding in my hands this moment, lo and behold, EVERY SINGLE TOILET sits back against a wall.

    Also, we measured and found that we only needed a 14" rough-in to fill the gap, so we went to the plumbing supply to order one. Interestingly, they are two-three weeks back-ordered. Is this due to lots of framing being in the way of the normal 12" rough-in, or a bunch of moron plumbers roaming the planet? (Present company excepted, natch.)

    Far be it from me to say, but I myself am something of a moron when it comes to construction issues, and yet I seem already to be more fluent with the code than the very expensive guys who did my plumbing job.

    Thanks to all here for the help.
    Jensie
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #12

    Nov 7, 2007, 07:04 AM
    Quote Originally Posted by jensie
    Also, we measured and found that we only needed a 14" rough-in to fill the gap, so we went to the plumbing supply to order one. Interestingly, they are two-three weeks back-ordered. Is this due to lots of framing being in the way of the normal 12" rough-in, or a bunch of moron plumbers roaming the planet?
    Actually, a 14" rough-in is a rarity, which would explain the three week wait.

    Manufacturers shut down their lines and re-tool periodically to fulfill backlogs of special orders.

    Believe it or not, you're actually quite lucky, some waits can be as long as two months.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #13

    Nov 7, 2007, 08:14 AM
    N case you missed it the first time here's what you can tell the next plumber that attempts to blow smoke up your skirt about keeping that toilet tank away from the wall.
    "There's a reason for the 12 inch rough in. We leave just a tad of give in a tank when bwe install it. This allows the tank to give a bit when you lean back on it. If the tank couldn't give and was tight against the bowl it would put a strain on the tank bolts and crack the tank. the wall will stop the tank before it can move back enough to put a strain on the tank bolts. Having too much play behind the tank would allow the tank to tilt back far enough to break the bolts right out of the china tank. Now this may never happen, but it could and that's why we take steps,( the 12" rough) to see that it don't". Good luck, Tom
    vinc12224's Avatar
    vinc12224 Posts: 3, Reputation: 2
    New Member
     
    #14

    Nov 16, 2010, 03:18 PM
    Then u shouldn't pay him cause that is a lie if it was done using the right measurements that wouldn't happen
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #15

    Nov 16, 2010, 04:45 PM

    Viunce,
    You're responding to a three year old thread, Notice the date in the upper left hand corner. Regards, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Distance from Wall to toilet drain [ 3 Answers ]

I am framing a basement batheroom that was roughed in when the house was built. The existing toilet drain seems close to the foundation wall. When I go to frame the finished wall what is my recommended and/or minimum distance from the finished wall to the center of the toilet drain? I can make...

Help! Toilet Too Close To Wall! [ 3 Answers ]

The toilet in our upstairs bathroom has been installed too cose to the wall. The lid to the bowl won't even go on completely because there is not any clearance between the back of the tank and the wall. I measured from the closet bolts (?) to the wall and it measured 11 1/2". What are my options...

Location of toilet and wall [ 4 Answers ]

Help! New house with roughed in drain lines in basement. After framing, toilet drain is 10.5 inches from bottom plate. I know that textbook should be 12 inches. What are my options? Thanks.

Help: Toilet tanks too FAR from wall. [ 3 Answers ]

Thanks so much for this site, it is very informative! We are about to close on a new construction home. This house is located out of state, and we just discovered that the 3 toilets have been placed 2½", 4½", and 6" away from the wall. The builder said they were placed that way because of the...

Max distance of vent to toilet [ 3 Answers ]

I am adding two toilets (1.5 baths) to the ground fllor of my house (which is a concrete slab. The house is in NJ. What is the maximum distance the toilets (WC's?) can be from the vent line (I'm using 3" drains and 2" vents). Thanks Mike


View more questions Search