    480 volt stepdown transformer
    I am currently working on a quote that requires me to add a step down transformer (480vac/208vac). I mostly deal with Low Voltage/Dc Power and do not have a clue about sizing the transformer. I am looking for someone who can help me size it correctly. I know that the source/line voltage is 480vac, the load current will be (2) 200amp feeds going to 208vac inverters. Also need to know the fuse size for feeding the transformer. I appreciate any help you can provide.
    drgall's Avatar
    drgall Posts: 1, Reputation: 1
    New Member
     
    #2

    Mar 8, 2011, 09:28 AM
    Normally you size a transformer based on secondary current requirements. In your case you have indicated (2) 200a loads at 208v. The following formula applies;

    KVA = IxEx1.73/1000 where I=current, E=voltage

    400*208*1.73/1000=143.936 KVA Transformers are available from many suppliers and you will find a 150KVA is a standard size for most.

    Fuse primary side at 225a

    (150*1000)/(1.73*480)=180.6*1.25=225

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I operate 230 volt machinery with 480/277 volt [ 7 Answers ]

480/277 volt 3 phase power is the proposed electrical service for a for a new building. Will I be able to power machinery that requires 230 volt 3 phase?

I have 480 volt, three phase available. Can I pull 240 volt, single phase off this ? [ 1 Answers ]

Have available 3 phase, 3 leads plus a ground. Need to run 240 volt, single phase connection off the 3 phase. Is this possible without a step down transformer?

480 volt transformer [ 4 Answers ]

Hi there, We are moving into a warehouse that has a 480 volt transformer. The transformer is located on the other side of our office wall. I'm wondering if there's any danger of radiation being so close to it. Thank you.

Size of stepdown transformer for 2400 watt 3.5 hp blender motor [ 1 Answers ]

Dear folks, I have a 110 v megablender with 3.5hp motor in New Zealand with 220 v power. Yes I know the cycles are different but I figured that one out and it's OK. The blender is 2400 watts. How big of a step-down transformer do I need. I was hoping that 3000 watts would be enough but then I...


View more questions Search