    One of my heating zones is not working
    I have baseboard forced hot water system with 3 zones. The problem is that the 3rd zone (upstairs) only kicks in when the 1 zone (basement) is working. I changed the thermostat in the 3rd zone but to no avail. I only have heat in the 3rd zone when the 1st zone is working.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 13, 2009, 09:44 AM
    Unless the 1 zone is a master zone (IE the other zone is tapped off the basement zone after the zone valve) you have a interesting problem. First make sure the boiler water pressure is high enough to operate the upstairs zone. Usually 15 psi max on the gauge will do it. If that checks OK if not adjust the pressure since no water for some reason is getting to the second floor due to lack of system pressure. Post back with results on the pressure reading for the next step if necessary.
    JibaroSoy's Avatar
    JibaroSoy Posts: 4, Reputation: 1
    New Member
     
    #3

    Dec 14, 2009, 07:50 PM

    Thanks for your quick response. Pressure checks OK. What is interesting is that the basement zone was the last one to be added to the system about 5 years ago.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 14, 2009, 09:15 PM
    With systems like this it is always possible to have many different items that can cause the same problem. Did you check the master zone thing? Does the upsstairs zone open when its thermostat calls for heat?
    JibaroSoy's Avatar
    JibaroSoy Posts: 4, Reputation: 1
    New Member
     
    #5

    Dec 15, 2009, 04:28 PM

    Yes, but only if the basement zone is active. If the basement zone is off, the upstairs doesn't open.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Dec 15, 2009, 07:58 PM
    If the basement zone has to be working before the upstairs zone will open as you mentioned then I would suspect a wiring or control problem. These type of items have to be checked ON Site since we cannot see your system from here. If you do not have the capability to test the electric part of your control system the you will have to hire local for on site service.
    JibaroSoy's Avatar
    JibaroSoy Posts: 4, Reputation: 1
    New Member
     
    #7

    Dec 16, 2009, 03:43 PM

    Thanks, this gives me a good direction to follow.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heating efficiently in 2 zones - heat pump and gas [ 2 Answers ]

I live in a 2 story (plus basement) single family home and am trying to determine the most efficient (energy and cost) way to heat my home in cold weather. I have 2 heating/cooling zones - a gas furnace which heats the basement and first floor, and heat pump for the 2nd floor, where the bedrooms...

1 of 3 heating zones not working could I have an air bloc [ 1 Answers ]

Could I have an air block and how do I fix it

Noise when 2 zones of radiant heating system used [ 1 Answers ]

When I start up 2 or more zones of my radiant heating I get a whoo whoo noise over and over. Any suggestions? I have already tried bleeding the air from the system. The system has a newer bladder system expansion tank. It doesn't happen with just one zone, only when a second is activated.

1 out of 3 heating zones not working [ 3 Answers ]

Our heating system seems to be operational... specially given the fact that 2 out of the three zones work like a charm. The zone that doesn't work uses a "Honeywell V8043 E 1012 motorized valve", and since the problem started, we've replaced the motor only... and it didn't work. Now, we've...


View more questions Search