Ask Experts Questions for FREE Help !
Ask
    AntonArcher's Avatar
    AntonArcher Posts: 5, Reputation: 1
    New Member
     
    #1

    Jul 6, 2010, 04:29 PM
    Brass drain installed incorrectly in pebble shower?
    Hi Experts.

    Thanks so much for looking at my question. I had some water damage on the ceiling one floor below this shower. I found some grout and caulk issues (holes) so I figured that's probably the issue. When I removed the caulk at the bottom edges of the walls, I found standing water below it. So I opened up the drain assembly and this is what I found:

    http://img5.imageshack.us/img5/299/dsc0088or.jpg

    Note the picture is huge so you can zoom in.

    The brass parts (AB&A #6420) were screwed together only a small number of turns, presumably to make the drain level with the stones. The rest of the space around it was filled with some decomposing putty (in the bag on the left.) The plastic ring (shown at top) and a fiber ring (in bag on right, decomposed) were installed as if the two brass pieces were going to be screwed together entirely. In other words, they were embedded in the putty and doing nothing. Everything was wet of course since there was nothing stopping the water from settling around the drain (in the putty.)

    Having read some of your other discussions, particularly about liners being wedged between two drain pieces, I suspect this installation is nonsense? The brass pieces seem designed to hold liner between them (snug) instead of being used as a spacer.

    Also, I can't figure out what the horizontal cut in the PVC pipe is.

    Could you please tell me if this install is just something fancy that I don't know about or if it is simply complete nonsense/hack?

    Thanks for your time,
    Anton

    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Jul 6, 2010, 04:59 PM

    Did your shower drain look like this or very close to it?(see image) The bottom part of the flange n goes first. Then the shower pan and the top half of the flange clamos over the drain.Back to you. You may then put the drain of your choice, PVC, Chrome or brass on then female threads of the flange. . There should be no putty involved as the flange has weep holes that drain out any water that seeps through the tile and mud to the pan. Was this job permitted and inspected? Let me know , Tom
    Attached Images
     
    AntonArcher's Avatar
    AntonArcher Posts: 5, Reputation: 1
    New Member
     
    #3

    Jul 6, 2010, 05:12 PM
    Hi Speedball.

    Thanks for looking at this. My drain consists only of the brass part that you see in my picture (lying on the ground towards the top of the picture) screwed into the bottom part, but only until it is level with the ground. That's why there is so much space left between the top brass plate and the stones, which is where all the putty was. Then a metal drain cover (disk) is screwed to it.

    I can make another picture with everything in place if you want.

    All of this work was done in a gut renovation before I bought the house. I suspect the flipper didn't care all that much as long as it looks right. I am very worried that this is going to need to be ripped up. Can you tell from the picture if this is the case?

    Thanks,
    Anton
    AntonArcher's Avatar
    AntonArcher Posts: 5, Reputation: 1
    New Member
     
    #4

    Jul 6, 2010, 05:25 PM
    Comment on AntonArcher's post
    PS: The exact drain part is model 6420 shown on page 11 here:
    http://www.abainc.net/PDFFiles/Brass.pdf

    Also, I could not find any weep holes anywhere.
    AntonArcher's Avatar
    AntonArcher Posts: 5, Reputation: 1
    New Member
     
    #5

    Jul 6, 2010, 05:27 PM
    Comment on speedball1's post
    Oops, sorry I posted my response as an answer below (by mistake)
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #6

    Jul 7, 2010, 07:17 AM

    Wrong drain. Has no weep holes. This type of drain as in your posted link is NOT to be used in showers. This is what happens:

    1. You open hot water
    2. Hot water hits cold pebble-covered shower floor
    3. Concrete condensates
    4. Condensation has no place to go ( no weep holes ) so it just sits around

    This is a common problem. It usually happens when inexperienced tradesman does the installation. If you want to correct it, you have to replace the shower drain with the one in Tom's post. Sorry, no way around it.
    AntonArcher's Avatar
    AntonArcher Posts: 5, Reputation: 1
    New Member
     
    #7

    Jul 9, 2010, 04:27 PM
    Comment on Milo Dolezal's post
    Understood. So your expectation is that I would have to have the whole job re-done to get this fixed? I just want to know what you think before I call a contractor and get surprised.
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #8

    Jul 10, 2010, 12:38 AM
    AntonArcher, you don't have to necessarily remove entire floor. It depends how skilled your contractor is. (S)he can cut 12" x 12" square, carefully remove tile and concrete, cut water proofing and remove the drain. Then, install new drain and water-proof the patch . Re-pour concrete and reset stone tile. But this has to be done by somebody who knows what (s)he is doing.

    However, if I am the contractor on the job, I remove the entire floor...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installed the shower pan and forgot to put in the shower drain first... oops! [ 8 Answers ]

I have a 3x5 fiberglass pan installed (built in with framing on top of it) and no way to get the drain attached. Argh. Is there any way to deal with this without ripping out all this work?

Shower pan leak with brass drain [ 1 Answers ]

I have a second floor fiberglass shower pan that has a leak that's been staining my ceiling below. I'm pretty sure the leak is coming from drain adapter. The water stain is directly below the drain adapter. The drain fitting is a B&K 133-301 drain. I'm pretty sure the leak is coming from the...

2" brass shower drain [ 1 Answers ]

Is there a tool that can take a 2" shower drain out without cutting the trap out? Stephen

Ripped brass pipe and shower drain [ 1 Answers ]

I am replacing a bathtub drain and overflow pipes with a cast iron two piece shower drain onto a concrete floor. Pipe is 1 1/2 inch and the cast iron drain is 1 1/2" . Unfortunately the brass bathtub slip joint was over 30 y.old and broke off during removal, so now I have it sticking 1/4" above the...

Oatey Brass No-Calk Shower Drain ?'s [ 0 Answers ]

I will be installing a 36" x 36" cultured marble shower pan over a wooden subfloor (I live in a condo) and plan on using an "Oatey Brass, No-Calk Shower Drain" (pn 42150) because I will not have any access from below during the installation process. Seeing that I cannot afford to have this...


View more questions Search