    Furnace blower can not auto start
    I have a problem with my furnace blower not starting automatically. It works good when I swiched the fan option to "ON", the furnace was burning and fan was running. However if I pick "AUTO", only the furnace burns periodicaly, and the fan totall gets stuck. I am wondering if it is a wiring problem, but not so sure. I will appreciate any help from anyone.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Oct 30, 2005, 04:54 PM
    You have 2 temperature limit switches in the furnace. One turns on the blower once it is hot enough when the furnace comes on. The second one turns off the gas if the blower fails to come on, or it gets too hot for some other reason. If the blower fails to start, the gas will keep coming on until the upper limit switch shuts it off.

    Some furnaces use a different relay and coil for a higher speed for fan only and A/C is you have it. This means the problem could be the relay too. Most of the controls on newer furnaces except the limit switches, are on a board making diagnose and repair difficult. If the limit switch seems to be working, you may be best off buying and installing a new board, hoping that fixes the problem. You could call a repairman, and pay another $100 in labor for him to replace the board. $$$$$$$
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #3

    Oct 30, 2005, 06:31 PM
    The fan worked very well in summer time when use A/C.
    [QUOTE=labman]You have 2 temperature limit switches in the furnace. One turns on the blower once it is hot enough when the furnace comes on. The second one turns off the gas if the blower fails to come on, or it gets too hot for some other reason. If the blower fails to start, the gas will keep coming on until the upper limit switch shuts it off.

    Some furnaces use a different relay and coil for a higher speed for fan only and A/C is you have it. This means the problem could be the relay too. Most of the controls on newer furnaces except the limit switches, are on a board making diagnose and repair difficult. If the limit switch seems to be working, you may be best off buying and installing a new board, hoping that fixes the problem. You could call a repairman, and pay another $100 in labor for him to replace the board. $$$$$$$[ Thank you very much. The interesting thing is fan worked perfectly in the summer time when I uesed A/C. At your point, there are 2 control systems to the fan for heater and cooler separately? ]
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #4

    Oct 30, 2005, 06:47 PM
    But how about that fan worked well in the summer time?
    Thank you very much, Labman. The interesting thing is fan worked perfectly in the summer time when I uesed A/C. At your point, there are 2 control systems to the fan for heater and cooler separately? By the way, where is the board, I checked manu and there is not a "board".
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Oct 30, 2005, 07:04 PM
    The older furnaces were much simpler and cheaper to fix. Start at the blower motor. Follow its wires back to the relay or relays. The relay should have 4 wires, one connecting to the power supply from the house, one to the motor, one to a transformer, and one to the limit switch. If you have 24 volts at the wires from the limit switch and transformer, power from the house, and the blower isn't running, the relay is bad. You may be able to confirm it is the problem by giving it a knock. If the blower starts, the relay is definitely bad.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #6

    Oct 30, 2005, 07:19 PM
    Thank you
    Thank you, I know where it is, and will work on it.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #7

    Oct 30, 2005, 08:15 PM
    Yes, you are right. My furnace was older, around year 1985. But I found 5 wires connecting to the relay instead of 4, of which 2 were connected to the limit switch. Do you know the 5 wires are right? :)
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #8

    Oct 30, 2005, 08:28 PM
    The fifth wire could be from the A/C. That makes it look like the limit switch could be bad. On the other hand, if it set for a while between the cooling season and when you needed heat, the relay could have stuck.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #9

    Oct 30, 2005, 08:49 PM
    Do you think it might be a problem of wiring on the limit switch? Someone repaired wires to A/C before summer came this year.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #10

    Oct 31, 2005, 08:53 AM
    Yes. The switches close when the air in the furnace heats up. If somebody
    Disturbed the wires to the limit switch. It would look like it was open, the air
    Not hot enough to start the blower. If you have a multimeter or a test light,
    Check the wires to the limit switch. With the power off, it should show
    Conductivity through the switch. Sometimes just bending a wire a little can leave it broken off inside the insulation.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Fan Blower will not come on in auto [ 8 Answers ]

Blower will only come on when in "ON" position. "Auto" position will not cause it to go on. One can hear the thermostat click (basically saying its time to kick in) but the blower will not commence until I manually set it to "ON". At first, I thought it was thermostat so I replaced it with a...

Furnace Manual Fan OK - Not Auto Though [ 1 Answers ]

I have a York Stellar Plus (15yrs old) with an Auto and Manual Fan Switch on the T-stat. The Fan will work when turned to ON (at the T-Stat) but it will not come on when you turn the heat on with the Fan switch turned to Auto. I have replaced the Limit Switch. No difference Thanks!

The blower doesn't start on "Auto" [ 10 Answers ]

Please someone help me. My furnace Lennox G20Q3/4E-100-5 behaves as follows: 1) Fan is on "Auto" 2) Thermostat calls for heat 3) Green light comes "On" on IPI module and then burner comes "On" 4) Flame occurs 5) Blower doesn't come "On". After a while, the burner stops due to safety. It...

Furnace won't heat in Auto [ 2 Answers ]

I have read the different posting and replys, but they don't seem to address my problem. Friend has an older Kenmore Power Miser 70 that has an old electronic ign. (no flame senser). The furnace will heat when the fan switch is set to "on" position, and it will cycle the heat. When the fan is...

FAN doesn't work when it's 'Auto', but works fine at 'On' in my central air/furnace [ 1 Answers ]

undefinedFAN 'On' or 'Auto'FAN 'On' or 'Auto' Hi, I have programmable thermostat connecting air condition / furnace system. Now if I turn system to 'Cool' and Fan at 'Auto', no cool air come out (compressor works, you can hear the noise). If I set FAN to 'On', life is getting better. But the FAN...


View more questions Search