    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #21

    Sep 29, 2009, 09:25 PM

    People almost always want to be able to turn lights in an out building on and off from the house. In other words you don't want to walk back out because you forgot to turn the lights off. Suggest you pull a 12/3 cable for a 3-way switch in the house for the shop lights.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #22

    Sep 30, 2009, 02:54 AM
    Grease, I said to use (3) #2 and (1) #6, never mentioned #4, as you have in your materials list.

    Medic, yes any feeder now needs an equipment ground, no matter in a detached structure or not.

    The 3 wire feeder is no longer allowed.

    On another note,

    This is as good a place as any to mention this, Table 310.15 (B) 6 of the NEC is not allowed for subpanel feeders. I had misused this table myself in the past. So, #4 copper, for example, cannot be used to feed a 100 amp subpanel, only to feed the main service.

    All experts, and any others that offer advice here, please take notice, and cease and desist from offering Table 310.15 (B) 6 wire sizes for residential feeders.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Size of wire and breaker to be use for 60kw heater [ 1 Answers ]

Dear sir Can you help me regarding the problem for 60 kilowatts heater to be used in my boss house

Wire Size for 250 Amp breaker 3 phase 208Y/120 [ 1 Answers ]

Wire Size for 250 Amp breaker 3 phase 208Y/120

100 amp breaker wire size [ 5 Answers ]

Will #2 aluminum wire fit a 100 amp cutler - hammer circuit breaker

Wire and Breaker size [ 2 Answers ]

I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?

Wire size in a 100 amp breaker [ 1 Answers ]

I was wondering if a 2/0 wire will fit in a siemens 100 breaker? Thanks for your help


View more questions Search