    #21

    Aug 29, 2009, 08:30 PM

    To re-iterate, you have a 240/120 V 4-wire circuit and a 120 V circuit.

    The only POSSIBLE thing you could do is to convert the 120V inverter output into a 240 center-tapped output by means of a transformer.

    Two high rated 7.5 KVA instead of 2, but this is similar to what you would need with correct outdoor enclosure, etc. SQUARE D 7S6FIS Transformer 7.5kva

    Grainger is Wholesale only.
    sailfast's Avatar
    sailfast Posts: 12, Reputation: 1
    New Member
     
    #22

    Aug 29, 2009, 08:41 PM

    That's more trouble than it's worth. Thanks for your advice. Guess I'll stick with the status quo.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #23

    Aug 29, 2009, 09:02 PM

    True, but you might be able to pick up the required transformer surplus - cheap.

    You need 2 KVA with a 120/240 input and 120/240 output such that you get 120 V in and 240 CT out.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #24

    Aug 30, 2009, 10:43 AM

    If not mentioned, Jumping both hots could cause overloading on a Multi circuit(2 hots sharing 1 neutral).
    If all you need is 120 for power outages, perhaps 1 leg would do, the one with most emergency circuits. Swap necessary ones from other leg to that phase as well.
    When placing a circuit on the opposite phase, be sure to place other multicircuit wire on other phase.
    sailfast's Avatar
    sailfast Posts: 12, Reputation: 1
    New Member
     
    #25

    Aug 30, 2009, 08:53 PM
    Quote Originally Posted by Stratmando View Post
    If not mentioned, Jumping both hots could cause overloading on a Multi circuit(2 hots sharing 1 neutral).
    If all you need is 120 for power outages, perhaps 1 leg would do, the one with most emergency circuits. swap necessary ones from other leg to that phase as well.
    When placing a circuit on the opposite phase, be sure to place other multicircuit wire on other phase.
    I don't see how this could cause circuit overloading. As I described earlier, the Yamaha generator is only capable of 2000w peak and 1600w sustained. Unless there's something I don't understand, the worst-case is I overload the generator and pop the protection circuit.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #26

    Aug 31, 2009, 04:12 AM

    Then you're fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

30 amp generator installed to a 60 amp transfer switch? [ 7 Answers ]

THis is the generator I want to install, 6800 Watt Portable Genearator ELECTRIC START # Wattage * Running Watts: 6800 Watts * Maximum Watts: 8500 Watts my plan is to mount a box on the outside of the house, with the 120-240V L14-30R inlet, so I can plug a extension cord if I...

Generator transfer switch [ 1 Answers ]

How difficult is it to install a generator transfer switch? It's pre-wired, doesn't look too Difficult. Is there anything I should look out for? The only thing I'm not sure of is it comes with two 15-amp 1-pole breakers, two 20-amp 1-pole breakers, and one 2-pole 20 amp breaker. How do I tell the...

Generator transfer switch - enough for well pump [ 1 Answers ]

I have a 10hp 5600 generator that I want to connect to a "GenTran 20216 Manual Transfer Switch". It states that this transfer switch has 6 switches (rated 15 amps ea), a handle tie for one 2-pole circuit such as a well pump. My question is this - my well pump is 220 30 amps. Does two switches at...

Generator power transfer switch [ 1 Answers ]

Our power goes off on a frequent basis. If it is off more than 8 hr I need to power up with my own generator 8kw, to prevent spoilage and to run the well. My question is do you have to disconnect the neutral also and run the neutral to the generator or can the neutral be common to both power...

Transfer Switch & Generator Compatibilty [ 3 Answers ]

I have installed a manual transfer switch in my home. It says in the instructions to make sure the neutral is un-bonded to the generator. My Generator has a bonded neutral to the frame. What can I do to make the switch and the Generator compatible? Thanks


View more questions Search