    When you jumper pressure switch, you need to wait until the inducer motor starts and reaches full speed and then put your jumper across it. Then your ignitor will glow, then burners should light. If ignitor glows and burners do not light, you may have faulty gas valve or bad control which is not sending 27volts to the valve. Pull wires from gas valve and start the whole cycle over with a volt meter across both wires set on ac volts, then wait for ignitor to glow, at this time there should be 27 volts read on meter. Be patient while waiting for 27v it takes several sec. If voltage is noted, then you more than likely have a faulty valve, make sure to re connwct wires and cycle again. If no voltage to valve, then control board is culprit, check 12 pin connector for secure connection. Hope this helps

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane XB1000 Compressor fan not working [ 4 Answers ]

I have Trane XB1000 A/C. Compressor fan is not running. The Blower fan is running. No cold air coming from a/c. Fan rotates freely when tried manually. I changed both fuses on the box. But still a/c is not working. Any help will be appreciated

Old Trane furnace fan not working [ 3 Answers ]

HI, We are having trouble with our old trane furnace.It has worked fine up until last year when it got really cold and a kind of drainage pipe froze but it was easily fixed.This year poses a different problem.Our blower(fan)is sueaking really bad.So bad in fact that we were afraid to leave it on...

Trane Gas Furnace just stopped working [ 2 Answers ]

I have a Trane XL80 gas furnace. It also has a heat pump for ref. Today, the temp in our home dropped and I noticed that the furnace was not working. I opened it up, and vacuumed it out, and have no idea why it started working. All was good! However, hours later, the temp is again...

TRANE XL80 Propane Furnace not working [ 1 Answers ]

TRANE XL80 Propane Furnace not working I have an older TRANE XL80 (1989) recently quit working. I discovered the ignitor was not glowing and traced it to a bad relay in the control module. I had the relay replaced, now the ignitor will come on and the unit fires up but will only burn for about...

Trane A/C Not Working [ 1 Answers ]

I attempted to turn my trane central air on at the thermostat by turning the power on and lowering the teperature, and NOTHING!! I automatically suspected that the circuit had tripped to I went to the breaker it was in the on position , so I flipped it and went back to the stat. NOTHING. I tried...


View more questions Search