    IdahoBiker's Avatar
    IdahoBiker Posts: 37, Reputation: 2
    Junior Member
     
    #21

    Jan 30, 2009, 07:45 PM
    Quote Originally Posted by KC13 View Post
    Say...is there a wire connected to "GH" on the circuit board?
    Just wanted to let you Guys KNOW that I Located a "Service Manual" (PDF Format) for the 397H Furnaces... So, "IF" anyone NEEDS it (all 16 Pages), I would be happy to Provide...
    I Finally Found a OEM Pilot Burner & Igniter (BOTH for $32.00 +FREE SHIPPING), putting it in right Now as a matter of Fact:confused: Wish I had found This Manual BEFORE I started this:eek:, probably took off More than I needed too... Oh well Guess I'll do some Cleaning.

    So What did You Guys say that I should Look for In the Wiring? :confused:
    I found some of the Problem (the Electrode was too far away from the Burner):( It was way past 1/4", more like 3/8" and Bent towards the Center)
    I removed the Flame Sensor, and Cleaned (But it wasn't too Bad)
    Will I NEED to Re-Adjust the Pilot Flame?
    Because of What I started this Post with, will I Need to Adjust the "Blower Off-Time Control"?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Older gas furnace is short cycling [ 32 Answers ]

I have an older Sears "Fifteen" horizontal gas furnace (#867767840) located in the crawl space. Recently it has been short cycling, meaning it starts a normal cycle, runs for approximately 1 minute, stops for several minutes, then starts another 1 minute cycle. This repeats until the set...

Furnace cycling [ 2 Answers ]

My newer energy efficient furnace cycles every 10 minutes about, I have a new one story home that is very well insulated.

Furnace cycling [ 1 Answers ]

I have a Trane gas furnace w/no standing pilot it's electronic. Anyway when the t-stat calls for heat it will fire up and the shut of within 5 secs. It will do this approx. 4 times before it will eventually lock itself out and the blower will continue to run not ever reaching setpoint. I know...

Furnace off and on cycling [ 1 Answers ]

We had an air bubble in the vacuum system, removed the clamp, blew in the tube, problem solved-thanks for everyone who looked!

Older Night and Day A/C will not turn off [ 1 Answers ]

I have an older model Night & Day brand Central Air Conditioner unit. The compressor is outside and the blower in inside. When I plug it in (the electrical outlet is in the closet with the blower unit) the fan will immediately come on. This unit is also the gas heater for winter. I can adjust the...