    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #21

    Jan 15, 2009, 09:26 PM
    OK I had a guy come over and check out the unit. We found capacitors not meeting spec and the unit when running is pulling 19 amps. He did replace the Run Capacitor and brought the system down to 12 amps.

    He said to replace the defrost sensor and defrost control system which is set to 45 degree I noticed. Even the blower capacitor is not meeting spec, I replaced that not even 2 years ago. But he did show me the read out and the computer doesn't lie. I guess I need to use GE or some good brands and not china stuff.

    Also the fan blades are to far from the coil, the blades are not even flush with the shroud.

    So this is where Im at and the freon is just fine right at 40, a little over he said.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #22

    Jan 16, 2009, 04:32 AM
    Yep the China crapacitors are junk but there are a lot of them sold. The fan blade location will sure make a difference in air movement and it should be located correctly. Glad you got it running.

    PS best capacitors come from Amrad engineering

    http://www.smallmotors.com/html/amrad.html


    http://www.amradcapacitors.com/

    They also make the Turbo capacitors but there regular capacitors for HVAC work cannot be beat. They are not real cheap but they last just about forever. We have been using them at the university when we do our testing to provide a base line to compare to the china junk.
    Sproket's Avatar
    Sproket Posts: 10, Reputation: 1
    New Member
     
    #23

    Jan 16, 2009, 11:55 AM
    I replaced the P291-2004 run capacitor but need to get the one that is daisy chained to it also. It is a little bigger. Anyone know the model #?

    I will climb back up and look.

    Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GE freezer coil freezing up unevenly [ 1 Answers ]

I have a Westinghouse Imperial ET18GKXSW02. The coil in the freezer gets an ice buildup at the first corner of the coil were the bi-metalic senser is located. The tubing is cold to that point. The reast of the coil stayes warm. No cold air but fan and comp. run

Spine Fin Coil on Trane [ 1 Answers ]

Looking at getting a Trane heat pump to replace an existing A/C unit. Heard some comments that the Spine Fin coil design Trane uses is difficult to keep clean and can actually clog up if not cleaned properly. I've heard good things about Trane overall but wanted to know if this design creates any...

Trane xl 80 heating system will not come on - below freezing outside. [ 6 Answers ]

Our Trane XL80 gas furnace will not come on. Turned thermostat all the way up and turned the fan to on. Nothing, no heat, now blower. Tried turning on the A/C and nothing happened. Followed the reset instructions and nothing happen. It seems to be dead. Help it is very cold outside, below...

Matching Coil - Trane XR-13 [ 2 Answers ]

Can someone give me a ballpark figure on the price of a matching coil for a new Trane XR-13 A/C?

Trane Variable speed w/hot water coil/Ac wiring ? [ 3 Answers ]

I've read many of the previous questions/answers, but haven't found what I need. Low voltage wiring is not my strong suit. My AHU has a hot water coil in it, that I plan to heat with a Voyager water heater. It has an A/C coil, and that works fine. Previous answers have said that I should find a...


View more questions Search