Kiss, I understand 2 diodes in series, with both Cathodes tied together will block AC but Pass RF?
Not really, what you were seeing was voltages below about 0.6 V for silicon would pass right through. So, that' not a frequency dependence. Just the magnitude of your RF signal was small compared to say 60 Hz AC.
I used to use Non polarized Capacitors to Pass RF, but Block AC?
Can you provide any input.
Bypass RF maybe. Usually this is a result of RFI, where you want frequencies above a certain value to bypass to ground, thus keeping the system free of RF induced noise or am I missing something?
|
|
|
 |
Uber Member
|
|
Oct 9, 2008, 08:23 PM
|
|
|
Their was some one down here that wanted ESPN about 15 years ago, Cable Company said it was too far(1000 ft), So I got permission from the Cable Company, and ran 1000 feet or RG 6 from the house to a Utility pole, I had an Isolation Transformer in the house, feed voltage down the Coax, to a 35? Db Amp(on utility pole), cut off the AC power cord, used chokes and capacitors to separate and pass the AC and RF.
Basically an Antenna Preamp on Steroids. (Voltage up, amplified signal back down)
|
|
|
 |
Uber Member
|
|
Oct 9, 2008, 08:37 PM
|
|
|
So, the capacitor is not a Filter(Polarized)?
Filter has many meanings low pass, notch, bandpass. A DC filter is really a ripple filter. It dampens AC oscillations.
AC caps are used in crossovers to pass high frequencies to the tweeters. They are also sold as "bass blockers".
In this transformer, no. I dug out a transformer design book which is really tough to understand and they just touched on CVT's. With come design notes.
(2*PI*f)^2*L*C = 0.76
And then later they offered a way to reduce the value of C by adding another winding because generally C is too large, but as usual, they don't do a good job explaining things. This compensating winding seems to connected in opposite phase with the winding that would normally be connected to the cap. So, with the compensating winding, the value of Cc cannot
be determined by the equation above.
Your also used to Constant Current Transformers. They are known as ballasts.
Wat they did mention though, as I interpret it is that the voltage across the cap is usually 1.4 to 1.6 times the input voltage.
Back to NP caps. Yes, I do believe the connection method you chose will work too, but you have to pick which circuit is appropriate. To get the lowest ESR (Effective Series Resitance) you would want to steer each half cycle through a polorized capacitor. Not good for audio applications, for instance.
|
|
|
 |
New Member
|
|
Oct 10, 2008, 09:13 AM
|
|
|
The cap in my situation is not used as a filter. It is non-polarized and in series with the secondary windings. Hope that makes sense.
|
|
|
 |
Uber Member
|
|
Oct 10, 2008, 09:26 AM
|
|
|
Do you have:
1. primary (120V)
2a: secondary Nc
2b. Secondary Nc'
These two windings are series opposed and the combination connected to a cap with value of C or 6 uf @ 600 V
3. A third winding for your battery charger?
Does the AC voltage to the charger circuitry come from (3) or across the cap?
|
|
|
 |
New Member
|
|
Oct 10, 2008, 10:03 AM
|
|
|
K-I-S-S,
Here's the detailed story on this troublesome transformer:
1.) There is a single primary whose two wires are fed by 120V directly from the plug.
2.) There are at LEAST 2 secondary windings because the one side of the secondary comes to a 3-prong rectifier (2 prong have the secondary wires and the 3rd is the DC output).
3.) There MAY be 3 windings on the secondary because the capasitor attached to the secondary appears to have a smaller gauge wire. It seems that the cap wires are 20 gauge while the power output wires from the secondary are 16 gauge.
4.) At first, I though that the cap was in series with one of these secondary widings but now you got me thinking and I do remember the cap wires being of a higher gauge wire - interesting.. .
5.) The AC voltage to the charger circuitry does NOT go across the cap. Both wires to the cap go directly into the transformer secondary windings.
Thanks again for everything!
|
|
|
 |
Uber Member
|
|
Oct 10, 2008, 10:30 AM
|
|
|
The CAP should either be attached to a secondary winding by itself with nothing else. -OR-
There are two secondaries that the cap is attached too, but it's still one winding. One of the windings is out of phase. That is a compensating winding so that the value of C can be smaller. Connections can be internal.
The power output wires should be the largest wire.
So, it sounds about right. Your making me want to PLAY with mine.
The cap and input wires will probably be about the same.
So, it's probably somewhat important to measure the input voltage and the voltage across the capacitor. I would bet, that if you excited the transformer with a lower voltage (with bulb) without the cap, you could get an idea of the winding ratios. I do have the possibility of doing that at 3A variable (0-120V) isolated and 10 A fixed isolated.
|
|
|
 |
New Member
|
|
Oct 12, 2008, 10:01 AM
|
|
|
Hey folks,
Not sure about the rest of you but I'm getting one heck of a great lesson on transformers! I have an update for you folks, complete with pictures. Hopefully, I will figure out how to include them. Here's what I found.
First, the secondary winding that provides the output voltage is a 16 gauge wire and is the inner winding of the secondary. Next, the outer winding of the secondary is a 20 gauge wire that is attached to the 5 MFD 650VAC cap. Finally, the pictures, if I can figure out how to include them.
The first picture, Transformer 1, shows you the size of the transformer. The second picture, transformer 2, shows you a side view of the secondary winding with the double layer of coils (one for the cap, one for the output voltage). Let me know what you think.
I ordered the cap from the surplus site you folks gave me. Thanks and, again, thank for the great lesson!
|
|
|
 |
New Member
|
|
Oct 18, 2008, 03:20 PM
|
|
|
Hey Folks,
Just an update on the transformer problem. I replaced the cap but pretty much got the same results. This is what I found:
1.) The output continues to be 5 volts, no change
2.) I figured out that it is the outer secondary winding, the one that is in series with the cap, that is heating up. The inner secondary winding that feeds the rectifier for output voltage stays cool.
3.) The draw on the 120 v side used to be 8.9 amps but is now 8.4 amps. Don't think this has any significance.
Conclusion: I have no idea what the he** is going on. Why is the output voltage on 5 volts when it is suppose to be 36 volts? What is causing this transformer not to perform?? It's killing me. Any ideas? Thanks for the continued help!
|
|
|
 |
Uber Member
|
|
Oct 18, 2008, 03:40 PM
|
|
|
I think the winding where the cap goes is shorted.
What's the voltage across the cap?
Time for the light bulb trick. Take a 40 W light bulb and solder wires to it, if you can't find a socket. Put it in series with the AC line.
Take out the cap.
Measure the voltages including the voltage at the primary. Where the cap goes and the secondary.
|
|
|
 |
New Member
|
|
Oct 19, 2008, 08:45 AM
|
|
|
Hey K-I-S-S,
Thanks for hanging in there with me on this transformer problem. Here's the latest. I did what you asked and here are the results:
1.) I installed a 55-watt light bulb (didn't have a 40) in series with the transformer's primary and put the juice to it. The light bulb lit brightly.
2.) The output at the secondary windings, the windings that goes to the rectifier, was less than 1 volt AC on both secondary windings. (Remember, I had two secondary windings that power the rectifier.) It didn't matter whether the cap was in the circuit or not. The voltage was the same - less than 1 volt.
3.) The voltage at the cap wires with the cap removed was 5 volts AC. Again, this winding is the outside winding on the secondary coil.
So, I hope you have some magic here because I certainly don't. Again, thank you. Your efforts are really appreciated!
|
|
|
 |
Uber Member
|
|
Oct 19, 2008, 08:45 AM
|
|
|
I Still think secondary has shorted windings.
Know anyone else with a charger like that?
|
|
|
 |
Uber Member
|
|
Oct 19, 2008, 12:47 PM
|
|
|
You didn't quite do the right measurements.
You missed:
What is the primary voltage when the winding where the cap was 5 volts and the bulb was in series with the primary?
And...
What is the voltage across the cap in the normal configuration (No bulb)?
What I want to see is the ratios of those two voltages. The bulb will drop the voltage on the primary.
|
|
|
 |
New Member
|
|
Oct 20, 2008, 02:17 AM
|
|
|
OK, I think I got it now. Here are the answers:
1.) Voltage across the primary is 10.2 volts.
2.) Voltage across the cap is 4 volts and it doesn't matter if the cap is disconnected. With or without the cap the voltage is 4 volts on the cap winding.
3.) The output of the secondary winding that goes to the rectifier is less than 1 volt, if that is needed.
Again, these readings were taken with a 55-watt bulb in series with the primary winding. Let me know if you need any other info. Thanks again for everything!
|
|
|
 |
Uber Member
|
|
Oct 20, 2008, 08:51 AM
|
|
|
Well, you missed one, but I don't think it matters. It would have been the voltage across the cap with no bulb.
It sure looks like you have a shorted primary. This was probably consistent from the get-go because of the high current at no load. Without any experience with actual measurements of a good CVT under these odd conditions it was hard to tell.
A 1:10 reduction isn't right and neither is a 10:4. Since both of these are wrong, the primary has to be shorted. The small gage wire is where there is likely to be problems anyway.
The CVT is a great way to get regulation cheaply for low current and that's why it was used.
I told you about the experiments with a stereo I made with the CVT and bass performance. I also purchased a 500 Watt sine wave AC voltage reguator and with a torroidal transformer, the sustained bass performance improved because of the better regulation.
That transformer will be Expensive. Your only real hope is a transformer on the surplus market.
For a 36V battery charger, you will be looking at a secondary that's not 36V. It does depend on whether a half wave or full wave bridge is used.
Hammond Greeting Cards & Promotions has the sizing equations.
You can estimate the secondary current by the wire gage and the specs of the charger.
A little education for both of us.
|
|
|
 |
Uber Member
|
|
Oct 20, 2008, 04:49 PM
|
|
|
Shouldn't you read 120 at primary, not 10.2 volts?
|
|
|
 |
Uber Member
|
|
Oct 20, 2008, 06:06 PM
|
|
|
Yep, but not when the transformer draws 9 amps at no load. I you do a little math like R=120/9 and 55=120/R, you get about 4 V. Not exactly right, but in the right ball bark.
If the winding was a "Normal" transformer, the bulb would not glow and you'd measure 120 V. The bulb limits the power to about the bulb wattage. Sometimes better than fuses. Remember when, there were glass fuses and you could screw in a light bulb and keep pulling stuff out until the light went out. When the light went out you found the shorted appliance.
Since the transformer is trash anyway, maybe he can try measuring the output with no capacitor and no bulb?
|
|
|
 |
Uber Member
|
|
Oct 20, 2008, 08:19 PM
|
|
|
Mmmm. Lots of info in the newsletters. They seem to do a poor job advertising their products and a bang up job advertising support.
Looks like the option is calling them for a replacement xformer.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Power is going to transformer but nothing is reading out. Is this a bad Trans?
[ 6 Answers ]
My Air Condition died. It is a Bryant 383KAV system. I had an electrician check if power was entering the system. Yes, with a Volt Meter it is. We noticed the Transformer was receiving power but it did not come out.
Question: Does it sound like the transformer is bad? Or am I looking at the wrong...
Wiring power transformer to furnace
[ 4 Answers ]
I have a lennox furnace & I am trying to replace my transformer. On my old transformer one side has a black wire coming out connecting to a black wire coming out of the furnace. On the same side there is a white wire connecting to a yellow wire on furnace. On the other side there is a red wire...
Connecting a power transformer to a light?
[ 8 Answers ]
Hi,
I have an outdoor lamp at my house that is/was using a power transformer for the lamp. First question: Why?
The wires on one of the windings has been ripped off the unit and the base of the unit is very rusty. I do not know the manufacturer or the specs of the unit. So, I bought one,...
View more questions
Search
|