    #21

    May 26, 2008, 12:41 PM
    Ron,

    A grounded conductor is still a conductor as was pointed out by Stan. You have to count the three conductors? Wouldn't you considered the 120 to be a derivative of the 240?

    The 120 VAC represents a line to Neutral, the 240 is the Line to Line connection.

    What is your formula for Ed?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #22

    May 26, 2008, 05:49 PM
    Don,

    Formula method:
    2KId/CM
    2=Two lenghts of wire to the load
    K=12.9 for copper
    I=Amperage
    D=Distance
    CM=Circular Mil

    You can also use Ohm's law to get VD.
    Yet, in this case you would need the conductors resistance.

    The formula would be:
    I(R)=VD

    Voltage drop is only recommended by the NEC, but is not required. What's recommended:
    -Max combined volatge drop for both feeder and branch circuit should not exceed 5%
    -Max on the feeder or branch circuit should not exceed 3%

    So this means. The conductor volatge (feeder only) drop on a 120V source would be: 120(.03)=3.6V then 120-3.6=116v recommended for the feeder.
    If 240, then: 240(.03)=7.2V then 240-7.2=233V recommended
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #23

    May 26, 2008, 06:16 PM
    I use Lectri-Calc for voltage drop.

    Much as I like math, the math to figure VD it too tedious for me. :D
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #24

    May 26, 2008, 07:58 PM
    A lot of simplifications come from 2 basic equations:

    R = pL/A; Resistance = Resistivity*Length*(Cross sectional area) and
    V= IR

    p=16.8 nΩ-m; yep nano-Ohms-meter
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #25

    May 26, 2008, 10:26 PM
    Don:

    This should give you an intuitive idea as to why you would not consider the conductors as 3. I made the math EASY by saying that each conductor has 1 ohm of resistance.
    Note that when a 240 volt load is connected you are dissipating 800 W and when a single 120 V load is connected your also dissipating 800 W. And when you allocate between all three conductors only 350 watts are dissipated.

    So, you can hopefully see that you must use 3% of 120 V because of case 2 which is the worst 120 V load case. In case 1, you would take 3% of 240, Case 2 and 3, 3% of 120.
    In case #1, assume the neutral wire isn't run.

    .... Amp...0hms......Power (I^2*R)
    L1... 20... 1... 400
    L2... 20... 1... 400
    N... 0... 1... 0
    Ptotal......................800 W Case 1

    L1... 20... 1... 400
    L2... 0... 1... 0
    N... 20... 1... 400
    Ptotal......................800 W Case 2

    L1... 15... 1... 225
    L2... 5... 1... 25
    N... 10... 1... 100
    Ptotal .......................350 W Case 3

    What this says is that with a 20 A protection device on a dual breaker, you cannot exceed 800 W.

    Remember used 1 ohm to make the math very EASY.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage drop [ 5 Answers ]

I will be running wire to my shop that is aprox 250' from the main elect box at the house. I would like to have 220 volts and 110 volts. The wire will be buried underground the average temp in my area in the summer is 100 degrees. What size wire should I use. I will be welding with a welder that...

Voltage Drop [ 3 Answers ]

I am trying to illuminate a tunnel about 3000' long temporarily with 9- 400 Watt Metal Halide fixtures spaced about 320' apart. I have a 120/240 generator single phase that I will use to back feed a 240/480 volt transformer to deliver 480 volts, single phase to the tunnel lights. At 480 volts I...

Voltage drop [ 1 Answers ]

The Voltage will drop after 150 meter wire ,how to sole the problem . Thanks to all

Voltage Drop [ 2 Answers ]

I have a 20 amp breaker;there are a total of 7 receptacles on this circuit with a 15 amp GFI on the first receptacle. The first 5 receptacles in line work fine, the last two receptacles which are approximately 70 feet from the 5th receptacle flip the 15 amp GFI off when plugging in a drill. I...

Voltage drop [ 2 Answers ]

How far can you run an electrical cord, that is plugged into a 20 amp circuit, and still run a circular saw? If the saw starts slowly, will that harm the saw?


View more questions Search