    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #21

    Apr 28, 2008, 02:59 PM
    This WHOLE thing is wrong from the get go, and for several reasons.

    1) You CANNOT feed a detached structure with more than one circuit. For this purpose a multi-wire circuit is considered one circuit.
    It is being proposed to run MANY circuits to this garage. NOT good.
    I am still uncler if this is detached or attached. If it is attached then this does not apply.


    2) Derating was brought up. For all practical purposes, over NINE CCC's (current carrying conductors) you must start to derate #12 THHN. It is involved as to why, but ten or more CCCs and you must derate to the point where you are under the "standard" 20 amps for #12.
    Keep in mind, the neutral of a MWBC (multi-wire branch circuit) does not count as a CCC nor do grounds.
    It is being proposed to run WAY more than nine CCCs.
    For instance, if he runs ten MWBCs, for twenty circuits, this is 20 CCCs and he MUST derate those circuits to 50% of 30 amps, or 15 amps.
    IF this is an attached garage, then you would have to run several smaller conduits with up to eight circuits, (even MWBCs) in each to allow each circuit to stay 20 amps.


    I can understand trying to save money and using something you have on hand, but butchering a job and doing things ALL wrong is NEVER a good way to go.
    If you are insistent on using the THHN you then have go the multiple conduit run route provided the garage is attached as I said.




    Quote Originally Posted by EPMiller
    I believe you will have to have 1 green grounding conductor for each circuit, so you will have to buy that wire.
    NOT true, you need ONE ground per raceway, based on the largest circuit conductor.
    So you can have 100- #12 wires in a conduit and you would only need ONE #12 ground.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #22

    Apr 28, 2008, 03:26 PM
    Quote Originally Posted by stanfortyman
    <snip>
    NOT true, you need ONE ground per raceway, based on the largest circuit conductor.
    So you can have 100- #12 wires in a conduit and you would only need ONE #12 ground.
    Thanks Stanfortyman. I will file that fact for future reference if needed. :)

    As to the original question, I think the garage is attached, and he did mention 6 or 7 circuits. That would be 12 or 14 CCCs, so he would get into derating unless he did the multi wire branch circuit setup.

    EPMiller
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #23

    Apr 28, 2008, 03:48 PM
    Heck, he could do four MWBCs in a 1" conduit and be all set.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #24

    Apr 28, 2008, 05:34 PM
    Strat, that makes no sense to me. I believe that he is limited to one supply cable into the detached garage. So that means one breaker off the SEP (100 amp - two phase) to supply 120/240 on the sub panel.

    LRA has to determine if the sub-panel can be on the outside wall of garage.
    All receptacles inside the garage need to be GFCI protected.

    Tommy, it appears that you believe I think you to be an idiot. That is absolutely untrue. I don't know anything about you. If I appear to be rude, I apologize, I'm from Da Bronx, NY and we are speak two languages. Manhattan English and Bronx speak. I promise you I am not trying to be rude. My concern is that you are not approaching this situation wisely so I ask you questions first to determine what you know or don't know.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #25

    Apr 28, 2008, 06:00 PM
    Had replied but didn't send post, but I said, "I thought it was attached, then reread
    "through my attic of underground"? Others felt it was attached also. Myself it was confusing , and I should have asked him to clarify.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #26

    Apr 29, 2008, 07:53 AM
    Tommy,

    I went back through all the postings and discovered that your garage is attached. That's a different ballgame. I was under the impression that your garage was detached. I apologize for my error.

    I'll go back and start over.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #27

    Apr 29, 2008, 08:18 AM
    Strat,

    The phrase, "through my attic of underground"? is a typo.

    It should read, "through my attic or underground."
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #28

    Apr 29, 2008, 07:36 PM
    Wow!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding wire to a conduit with wires. [ 5 Answers ]

Is there a good way to pull additional wire into a conduit with wires existing? Less than 25 feet in length 2 90 degree sweeps 1 1/2" conduit with 3 large wires exist, probably #6, don't know for sure but plenty of space for the 2 #12 I would like to add.

3 wires + 2 wires  POOL MOTOR [ 2 Answers ]

I need help connecting a motor for my pool. The motor has 3 wires coming out of it. 1 white, 1 black, 1 black with a white stripe. A continuity test on the 2 blacks says they are wired together somewhere. I have a power cable coming out of the ground. 1 white + 1 black cables inside. ...

Thermostat Wires - Only 2 Wires (both black) [ 4 Answers ]

Hi there, I'm switching my thermostat for a newer digital one, though when I took out the old thermostat, there were only 2 black wires with white stripes on them. The new thermostat calls for an RH wire and a W wire, but I have no way of distinguishing the two apart. How can I tell which wire...

Hampton Bay remote wires do not match fan wires [ 1 Answers ]

Yesterday I installed a new Hunter ceiling fan. I also purchased a Hampton Bay wireless wall switch. Everything went well until I wired up the remote receiver. The receiver has a blue wire for the light that is supposed to connect to the blue wire (light) from the fan. The Hunter fan does not have...


View more questions Search