    #21

    Feb 16, 2008, 08:21 AM
    Recap;
    This occurs when no water is being used.
    The only thing that seems to make it stop closing the valve on the water heater inlet.
    The heater is approximately two years old and this did not occur prior to renovations.
    Turning off power to heated has no effect.
    There is no recirculation pumps or "instant hot water devices" installed.

    Are all of the pipes CPVC or or part copper and part CPVC?

    There is no recirculation pump, is there a recirculation line? May sound like a strange question but that's the set up I have, where gravity and syphoning cause the recirculation.

    At this point I would suggest that the vibration is in the water it self, not the pipes because closing the cold water valve on the heater is the only thing that will cause a change.

    Suggest turning off main house valve to eliminate outside world. If vibration or pulsation is there with main valve closed the source has to be in the house.

    After thought, do you have fridge with ice maker, or water dipenser, could something there be causing vibration.
    trix2's Avatar
    trix2 Posts: 14, Reputation: 1
    New Member
     
    #22

    Feb 16, 2008, 09:47 AM
    The renovation is CPVC and original house is copper. I isolated most of the new plumbing, CPVC, but the vibration continued.

    I'll have to check on the gravity and syphoning. Need to check what was installed and see if anything could cause that problem. This may be the answer

    Closed the main house valve, pulsating still exists.

    Closed the frig ice maker valve. Pulsating still there.

    I turned off the cold water inlet valve to the water heater to revarify the pulsating stops. It stopped.

    Would an expansion tank installed on the cold water inlet side of the water heater help?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #23

    Feb 16, 2008, 04:08 PM
    Cold water input of heater is connected by a flex pipe to CPVC. Stop valve on the CPVC right? CPVC added to existing copper from main line into house right? I'm guessing water heater was relocated.

    If it is indeed the vibration in the water, or water movement within the pipe, and not the pipes themselves, as suggest by it ceasing upon closing the heater input valve, we have eliminated the outside world and source must be in the house.

    Please close valves at each fixtures, one at a time, and see if you can cause a change.
    trix2's Avatar
    trix2 Posts: 14, Reputation: 1
    New Member
     
    #24

    Feb 16, 2008, 04:27 PM
    Your assumptions are correct except the water heater was not moved. The water heater is on a wall ajoining the new construction so the CPVC came to the water heater.

    I'll start turning off valves and post the results when I finish.
    Thanks
    trix2's Avatar
    trix2 Posts: 14, Reputation: 1
    New Member
     
    #25

    Feb 17, 2008, 02:57 PM
    The first toilet I isolated seemed to solve the problem. I may have others but this seems to be the fix.

    Thanks to all that helped.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #26

    Feb 17, 2008, 03:49 PM
    Tell us more. You mean to say that a loose washer in a toilet cause all this?
    trix2's Avatar
    trix2 Posts: 14, Reputation: 1
    New Member
     
    #27

    Feb 17, 2008, 05:23 PM
    My plan was to close each water valve a one at a time and see if it made a difference. When I closed the first toilet shut off valve the pulsating stopped. I kept the valve closed all night and then replaced the toilet fill valve and opened the shutoff valve this morning. So far I haven't heard or seen any pulsating. Last night was the first night in about 3 weeks I haven't heard the noise.

    Flushing the hot water may have helped some.

    I still may have similar issues but following the suggestions above I hope I'll be able trace them down.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #28

    Feb 18, 2008, 07:20 AM
    Kudos and congratulations on a great job of analyzing and tracking down a difficult problem. Give yourself a pat on the back and two weeks vacation.
    I love it when a asker. Especially a female, can go in and do a job just as good as a licensed plumber. GOOD JOB! Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pulsating sound in water pipes [ 4 Answers ]

Had to convert a room to a HCP accessible full bath... about the same time the house developed this pulsating thumping on the cold water side... all faucets/ toilets when they use water, I get a pulsation that is about equal to .01 galllon frequency (I had a walkie talkie in the house and watched...

Pulsating/knocking water in shower pipes [ 7 Answers ]

I just installed a Danze shower unit with valve model D113000BT and I'm having the same problem with pulsating and knocking when someone uses the sink. I pulled the valve apart and checked for debris and there was nothing. Could it be that the spring in the diverter is not strong enough? Please...

Pulsating sink sprayer [ 1 Answers ]

Hello, I installed a new Moen faucet last weekend. It is the type that has a separate lever from the faucet, a soap dispenser and a sprayer. So, there are four components on the sink. When I lift the lever to turn on the water, the sprayer starts pulsating (very vigorously I might add). If I...

Pulsating water [ 7 Answers ]

I have a 2yr old, 2 story home. I returned from Iraq about 6 months ago and noticed that at times the water will pulsate as it comes out of any fixture. I don't remember this problem existing before I deployed but it certainly exists now. It does not occur all the time and at times it is more...


View more questions Search