I was bored the other day so I went through all the postings for this issue. It seems that a lot has been done without finding out the cause of the problem. Also, there may be others in the same boat. So... using my computer geek background (I am a business analyst) I put together the following:
Recommendations made so far:
1)Replace HWH as it is near it’s end of life, if not over.
a.Unable to replace at this time.
2)Flush HWH
a.Unsure if done or results if done.
3)Clean out each faucet after flushing tank and while flushing lines to faucet.
a.Unsure if done or results if done.
4)Replace Diptube as it may be either clogged or melted.
a.Unsure if done or results if done.
b.Also, diptube only melts while join is being soldered, not overtime as HWH is not hot enough to melt plastic.
5)Clean out inlets to HWH.
a.In process after discovering it was a ball valve and not globe valve.
Here are some things that could help in diagnosing the problem:
1)Is the CW supply pressure to the HWH the same as it is to a sink?
2)What is the size of the CW supply?
a.To the tub?
b.To a Sink:
i.How do they compare to the HW supply?
3)Is the pressure comparable between the inlet and outlet on the HWH?
4)Is there a change in pressure if the WC is flushed?
5)Are you on City or Well water?
6)Trace CW inlet.
a.What is the first thing to connect to the CW line?
1Check the pressure to the incoming side of the point of use (POU) against the outflow.
2Check the pressure to the incoming side of the first POU against the pressure incoming to the HW htr.
ii.If the first unit is the HWH.
1.What is the next unit after the HWH?
2.What is the pressure at that POU?
3.How does it compare to the incoming pressure at the HWH?
7)What is the inlet size to the HWH?
a.Does it reduce from the mainline?
b.Does it reduce after it goes to the HWH?
8)What is the outlet size from the HWH?
a.Is it the same as the incoming?
b.Does it reduce after going to the next POU?
Suggested course of action:
1)Flush HWH and replace the small hosebib with a full flow ball valve
a.If needed, knock loose any sediment using wooden/plastic stick that remains at the bottom of the HWH.
2)Flush out each lav after flushing out the HWH.
a.Remove aerator and turn on water supply to purge lines.
b.After lines are purged of air. Shut off each faucet in turn
i.Remove both H and C control cartridges and clean them
I
i.Turn on supply to the faucet to flush out the lines and then shut off supply.
iv.Open supply line and flush lines again.
v.Clean and replace aerators
c.Go to next lav and repeat.
3)Did this resolve the pressure issue?
4)Using the supply diagram from tracing the water supply. (See # 6 in requested info section).
a.Check the pressure on the first POU.
i.How does it compare to the HWH outlet?
b.Check the pressure on the second POU.
i.How does it compare to the first POU?
ii.How does it compare to the HWH outlet?
c.Does opening the CW supply on the second POU impact the HW supply on the first POU?
5)Is there a change in the pressure on the cold side if more than one faucet in use?
a.If you are on well water, this could be a problem with the pump.
b.If city water, there may be a problem with their supply to your house.
Hopefully by now you will either find out where the source of the pressure drop is. And hopefully WHAT is causing it as well.