    Sep 25, 2007, 08:23 AM
    OK, sorry, did not see that. This thread is getting large and off topic a bit.

    So your pulling #4 for a 70 amp feeder? This will need a min of #8 EGC.

    I cannot find where is was suggested to not use an EGC and only use a ground rod, too much to review I guess.

    It does not matter, the good thing is your persistent with chasing me down and asking questions.

    With using a 4 wire feeder that includes an EGC, a ground rod is not needed at the subpanel.

    While a 3 wire feeder with ground rod is now allowed, it will be discontinued in the next code edition 2008. So may as well be ahead of the code, int his respect.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring to sub-panel. [ 1 Answers ]

Will this work properly if when wiring a sub-panel for 240v can one of the 3 aluminum 4 gauge wires in the pvc underground pipe be used as the neutral wire if that wire is bare? I intend to attach the ground bus at the sub-panel to a ground rod using 6 gauge bare copper wire.

Welder Wiring / % of Panel Capacity [ 3 Answers ]

I recently purchased a Lincoln Precision TIG 375 welder(here) at a business liquidation auction. It came with huge pin type connectors (shudda been a hint). After I got it home and read the manual, I discovered it requires a 175 amp breaker when used to it's max capability. I have 200 amp service...

Main to Sub Panel Wiring [ 3 Answers ]

I received an answer prior to wiring this up, but am a bit confused. I think I was told to keep the ground separate at the sub panel but am not sure. If so, I only need to pull 3 wires (2 hot legs and 1 neutral). I have attached my PDF for your review. Thanks, ...

Sub panel wiring [ 1 Answers ]

I have a 50 amp GFCI breaker in my subpanel box to be used by a hot tub. I noticed that the breaker has a post for the neutral wire load. Is it necessary to use this post or can my load neutral wire be connected to the neutral bus (same as breaker pigtail and supply neutral)?

Sub panel 40 amp wiring [ 1 Answers ]

I have a 70 amp sub panel. I'm trying to figure out how to wire in a 40amp breaker in the sub from the panel in my house. I have two hot wires coming in to separate lugs, one neutral, but the breaker itself has one trip/reset lever yet has two screws on the bottom of the breaker;one on each side....


View more questions Search