    Receptacle Tester Says Open Ground
    Please advise as to why R2 would show open ground using a receptacle tester.
    All three connections on R2 seem secure.


    R1 shows correct wiring.


    S1 is old time switch with no ground.
    The ground wires are bound together in old plastic box.
    Attached Images
     
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jul 23, 2017, 08:01 AM
    There are several possible reasons.

    1) While the ground wires are connected in the plastic box, the ground wire may be open between the panel box and the junction box.
    2) The main panelboard may not be properly grounded.
    3) Improper "Bonding" could cause a problem if the metal ground you are using is not bonded with all the other pipes and then to the electrical ground.
    4) Defective circuit tester.
    draftd's Avatar
    draftd Posts: 23, Reputation: 1
    New Member
     
    #3

    Jul 23, 2017, 08:22 AM
    If 1)
    Would not R1 also show open ground ?


    If 2)
    Would not all receps show open ground ?

    Went around the house checking all easy accesible receps and R2 is the only one
    showing the open ground.


    R2 has a lamp and adding machine plugged in and used almost daily.


    Is this a dangerous situation ?

    Thanks very much for your reply.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jul 23, 2017, 12:17 PM
    No so dangerous with what you have plugged in. A Lamp will likely not have a Ground terminal, 3rd prong of a Drill for example will connect to the Housing of the drill, if you drilled into a live wire, or a hot wire breaks loose inside and touches case, it will trip breaker, Not become Live.
    If a Plastic Box, it may just need a small pigtail(jumper) to restore the ground.
    A meter with 1 wire on hot, and the other on ground wire should show 120 volts.
    Ground and Neutral are Physically connected at Panel. Difference is, Neutral carries current, Ground is to keep things from becoming live.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Jul 23, 2017, 12:42 PM
    Does R2 come from R1 or the J Box? Could be a loose ground in either one.
    I just found an ungrounded outlet in a house with ground connected and the ground came from a switch box. Opened box and found loose wire, looked like it was never connected. Wire nutted to box ground and solved the problem. This was the only outlet showing no ground.
    draftd's Avatar
    draftd Posts: 23, Reputation: 1
    New Member
     
    #6

    Jul 24, 2017, 12:13 PM
    @ Stratmando
    R2 hot wire and ground shows approx 25v.


    @ ma0641
    I believe R2 comes from junction box.
    Opened R1 and it has only one wire.


    I cannot get to the junction box, which I guess is the main problem now.


    It was put in place when part of a brick wall was torn down
    to enlarge a exterior door and to setup a recep for a generator.


    I checked that all worked before closing up the brick wall,
    but did not test it correctly to catch the open ground.

    As mentioned, R2 is pretty much used daily.
    Lamp. adding machine, laptop (3prong) for about 3 years now.

    Sw1 and R1 are on the outside brick wall.
    R2 is on an inside wall.

    Pretty sure I could get a new line to R2.
    But what would I do with the screwed up line there now ?


    Thanks for the replies.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Jul 24, 2017, 06:58 PM
    If you get a new wire, wire nut and tape the old hot and neutral out of the way, connect old ground to new ground.
    draftd's Avatar
    draftd Posts: 23, Reputation: 1
    New Member
     
    #8

    Jul 27, 2017, 01:16 AM
    Thanks ma0641.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is an open ground at gfci receptacle? [ 2 Answers ]

New home and requested to be repaired by inspector before home sales.

Can a receptacle ground be attached to white nuetral terminal for ground? [ 1 Answers ]

I have older house. The receptacle showed "open ground." I connected a wire from the green ground terminal to the nuetral terminal, and the meter read "correct." I left it that way because everything worked. Is it safe?

Do you install a 120v 15 or 20 amp receptacle ground up or ground down? [ 15 Answers ]

Does the code have any stipulations on ground up or ground down? If so Prove it. An I am not talking about local ordinances nor the authority having jurisdiction. Simply the NEC.

Weird receptacle tester readings [ 1 Answers ]

When using a standard 120V receptacle tester on all receptacles fed from a 600V/120V transformer all three lights appear. There is no indication of what this means. When tested with a multimeter all readings are proper. Receptacle tester is working properly when pluged into plugs from other...


View more questions Search