    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #1

    Jul 3, 2009, 06:32 AM
    Split 220/240 volts
    Hi guys

    What are ramifications of splitting a 220/240 volt circuit between 2 double mini breakers?

    Use the bottom of one mini double and the top of the double mini below it.

    Can a strap be put on the trip switches to make it function the same as a full size 220/240?

    Back ground info

    Have 2 full size 15 amp 110 breakers each with #14 wire.

    Have a full sized double 15 amp breaker with #12 wire.This breaker does not have a 220/240 bar tying the trip switches together. Color of wires is black and red. I think it should have a tie bar.

    Purpose

    Would be adding 50 amp 220 breaker in place of double 15 amp breaker.
    Move wire from full size 15amp 110 to top of one mini double breaker.
    Move wire (red) from full size double 15amp breaker to bottom of 15 amp mini.
    Move wire (black) from full size double 15amp breaker to top of 15 amp mini.
    Move wire from full size 15 amp 110 breaker to bottom of mini.


    2nd alterative would be to put in a 50 amp sub panel. Would need info on doing this.

    Tks

    Chuck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 3, 2009, 06:58 AM
    Any 240 volt breaker must have a tie between poles. If one leg has a short or overcurrent, both poles must trip to de-energize the entire circuit.

    Certain brands make a full size 2 pole breaker with 4 poles, two inner tied and two outer tied. Murray comes to mind. What brand panel do you have?

    No one makes an accessory tie that you looking for, that I am aware of.

    http://cmsapps.sea.siemens.com/murra...y_02/02_07.pdf
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #3

    Jul 3, 2009, 09:06 AM

    I have a GE Cat# TRM2010S Model3
    100 amp service. Believe it is vintage 1972, when house was built.

    I have the material to make a tie bar.

    Would it be a problem if I tied the lower on one mini to top of other mini?

    Tks

    Chuck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jul 3, 2009, 09:56 AM
    Making your own parts is not allowed, all electrical material in the USA must be UL Listed.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #5

    Jul 3, 2009, 11:06 AM

    What if I take the tie off another switch?

    Chuck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jul 3, 2009, 12:55 PM
    Now you have me confused, are the two breakers next to each other? I thought they were apart with other breakers in between?
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #7

    Jul 3, 2009, 01:20 PM

    I will have 2 double minis next to each other.

    Will use bottom of one and top of other for the 220.

    See post #1 under purpose for total layout.

    Chuck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jul 3, 2009, 01:26 PM
    So you have a handle tie from Murray or similar? If it fits on the GE TQL handle, then go for it. I am not sure it will fit properly.

    Try to test it by only pressing on one handle to confirm it opens the other breaker quickly.

    Really better to use a real 2 pole breaker, as they are built with internal common tripping mechanism to insure both poles open due to a problem.

    There is always a chance that your method one pole can open due to an event, but not actually open the other pole, thus leaving voltage on a circuit with a problem.

    Don't you just hate electricians? We got a reason for everything.

    All for safety.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #9

    Jul 3, 2009, 03:45 PM

    My alternative is to put in a 50 amp sub panel.

    Could u give me step by step for doing this?

    The sub panel would be within 1' of main and hold 2 -15 amp 110 breakers and 1 -15 amp 220/240 breaker.

    Chuck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Jul 4, 2009, 04:41 AM
    Mount a subpanel, feed it with 3- #6 wire for the two hots and one neutral and 1 #10 green for equipment ground, feed it with a 50 amp breaker.

    Beyond that I don't do step by step instructions.

    Get back with a plan or diagram and we can help with the details that may be incorrect or missed.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #11

    Jul 4, 2009, 05:36 AM

    Thanks TK

    That's all I need. Really appreciate all the time u spent with me.

    Chuck

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wall mount A/C, 110 volts vs 220 volts? [ 9 Answers ]

I live an an 580sq ft apartment, & I know some of the other tenants have 220 volt A/C, & some have 110 volt A/C. Which is better & Why?? :confused:

What is the difference between 110 volts and 115 Volts? [ 5 Answers ]

What is the difference between 110 volts and 115 Volts?

How to Convert Any Appliances from 220 Volts to 110 Volts [ 2 Answers ]

How to convert appliances like irons, fans and other appliances from 220 volts to 110?

220 volts to 120 volts [ 5 Answers ]

I currently have a 220 volt/30 amp service to an electric washer/dryer combination. The washer/dryer broke down and I will be switching to individual units each requiring a 120 volt/15-20 amp supply suggesting a separate circuit. The current unit had a four wire configuration (2 hot -...

120 volts vs 240 volts tools [ 3 Answers ]

How do I configure a 120 volts 60hz woodworking tools bought in the usa to work on a 240 volts 50hz power rating in my country without having to compromise the motor operation. I understand that the stepdown transformer can only reduce the voltage but not the cycles. That means that a tool with...


View more questions Search