    Ground Fault Current At Main Service
    Here's a weird one. I have a tenant with a 150A, 3-Phase, 480V service. The main switchboard is in the basement and the breaker panel is located in the tennant's space 50 feet away. There is also a 120/208 panel board next to the 277/480 volt panel in the same closet. The step-down transformer is suspended above.

    Twice in the same year faulty HVAC equipment (480V 3PH) has grounded out and instead of tripping the branch circuit breaker, blows the main fuses in the basement. Once it was a 30 amp A/C device, the second time 9 months later it was a 60 amp duct heater. Again, neither time did the branch circuit breaker(s) trip, instead the main fuses blew. I don't suspect that the circuit breakers (newish) could be faulty although I have not had them tested. Could there be a grounding/neutral issue that is causing this problem... or possibly something else other than faulty breakers? Thanks.

Check out some similar questions!

Ground/Neutral Bus in Main Service Panel - Is there a Difference? [ 8 Answers ]

I'm preparing to provide new wiring to a sizable addition to a log home. Prior to beginning the new work I mapped my existing circuits thinking it best to correct any potential overloads in the existing panel/circuit design before introducing any new problems on my own. Decided to make a few...

Service disconnect and main neutral/ground [ 2 Answers ]

This is correct assuming that we are talking about a residential service, and that you do indeed have a main breaker in that panel. By main breaker panel I mean that there is a circuit breaker in the panel that when shut off will disconnect power to all the circuits in that box. If this is true it...

Short circuit current fault [ 1 Answers ]

I have quite a simple system. Contains one substation, feeder pillar and 3 houses. I have calculated the short circuit current that the transfromer in the substation can deliver but is there any one that can help me with finding the equations to calculate the short circuit current level supplied by...

Ground Fault [ 1 Answers ]

I wired my garage a year ago. Now all of a sudden I had a ground hot reverse alternating to normal in my outlets and my lights stop working properly. I rewired all the outlets and the it went away until I went to turn on a light. Then it went back to ground hot reversed. I had a buddy come over and...


View more questions Search
 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.