    Thermostat Heat works, A/C does not!
    I have installed a Hunter Programmable Thermostat model 44660. The heating works fine, but the A/C does not work. According to the display, the air is running, but nothing is coming out of the vents. While I know that the wiring colors are not always 100% accurate, I have the wiring set up as follows:

    Red - RH
    Blue - RC
    Yellow - Y/G
    White - W/B
    Green - G

    Any thoughts?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Mar 27, 2008, 05:40 PM
    Yep. Only heat will work as you have it. What were the terminals you replaced?

    You may have just had an R terminal in your old stat, in which the instructions should have said connect Rh to Rc and connect to Red.

    Blue has a number of possible functions or may not be connected.

    100% correct means the red wire is red etc. Right? <G>
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    Mar 27, 2008, 06:55 PM
    The way you have it wired is for a two transformer system. If you have a real old system or a commercial system it may run on two transformers. If not you need to jump the RC and RH. What did the blue go to on your old thermostat?
    matthewfort78's Avatar
    matthewfort78 Posts: 3, Reputation: 1
    New Member
     
    #4

    Mar 28, 2008, 06:35 AM
    Quote Originally Posted by matthewfort78
    I have installed a Hunter Programmable Thermostat model 44660. The heating works fine, but the A/C does not work. According to the display, the air is running, but nothing is coming out of the vents. While I know that the wiring colors are not always 100% accurate, I have the wiring set up as follows:

    Red - RH
    Blue - RC
    Yellow - Y/G
    White - W/B
    Green - G

    Any thoughts?
    The system is a new carrier system, the house was built in 2006. The old thermostat is a very simple carrier thermostat where:

    Red - R
    Blue - C (I'm assuming Cyan)
    Yellow - Y
    White - W
    Green - G

    In the instructions for the system, it said for 5 wire systems to not jump the RC and RH. The being said, should I try to jump the RC and RH?

    I did re-install the old thermostats last night and everything is working well. At least I know that this is not a A/C or system issue, just a user installation issue. I still would like to put the programmable ones back in. Below is a link to their manual showing not to jump the 5 wire system as a reference. Let me know what you guys think I should do. Also thanks for the help on this. I really appreciate it.

    http://www.hunterfanhq.com/tools/sal...ners/44008.pdf
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Mar 28, 2008, 07:53 AM
    The being said, should I try to jump the RC and RH

    Try it should work
    ahshabon's Avatar
    ahshabon Posts: 1, Reputation: 1
    New Member
     
    #6

    Apr 17, 2008, 08:26 AM
    Matt/All,

    I wonder if the jump solved the problem. I have the same problem with the Hunter 44660. I get either the heat or the AC to work when I connect the red wire to either the RH or RC! Would the transformer break if I jump the RC and RH? I also have a sixth wire "Orange" which I connect to Y/O!

    Thanks,

    AH
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Apr 17, 2008, 08:33 AM
    If you never had Rc or Rh in the past connected to two different wires, then the transformer won't break. The instructions for the stat probably mention to jump Rc and Rh. Some instructions tell you to remove a jumper when you have two transformers. The c and h refer to cool and heat, hence this is the reason why only one works when you move the wire between Rh and Rc.
    matthewfort78's Avatar
    matthewfort78 Posts: 3, Reputation: 1
    New Member
     
    #8

    Apr 17, 2008, 01:28 PM
    Ahshabon, I actually returned the units and plan on buying better Honeywell units in a couple of weeks.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC works Heat doesn't [ 4 Answers ]

Not sure why when I turn on my AC the unit comes on. When I flip it to heat, nothing happens. It worked the other night and I stayed warm. Woke up this morning freezing. Anyone have any ideas... suggestions?? I checked the breaker box and nothing was tripped. Thanks!

My dryer only works on low heat and not on high heat. [ 1 Answers ]

I have Whirlpool dryer model #TEDX640EQ1. The dryer does not produce any heat when on the high heat setting, but will get warm on the low heat setting. I need the high heat setting to work so that it doesn't take 2 cycles or more to properly dry my clothes. Anyone know what the problem could...

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Heat pump thermostat Aux. Light is going on when no resistance heat used. [ 2 Answers ]

I have a Maple Chase SaverStat thermostat on a Lenox heat pump. The thermostat and heat pump are ten years old. Recently when the heat pump comes on the Aux. light on the thermostat also goes on (not the emergency heat light). I have checked and the auxiliary heat strips and they are not heating...

Kenmore works just no heat [ 9 Answers ]

Yes I have a kenmore dryer that I bought out of a classified add Model number 110.86870100 I reset the breaker and made sure it was on heat not air but it still won't work I checked to see if there was any air flow coming out of the vent there is though I don't know how much air should be coming...


View more questions Search