    Upgrading to 200 amp service
    I want to upgrade from 150 to 200 Amp service. My current panel has double breakers in ever slot except where the A/C, Dryer and Range are connected. I have wired panels before but never upgraded the service. I have studied and planned the change over the last two months but I still have a question on the grounding. Currently my panel is a main breaker panel and it is grounded to the water pipe (No Grounding electrodes). My service comes in approximately 70 feet from where my panel is located. I am replacing the meter box with one that has the meter on one side and the 200 main on the other. I am running 4 awg 4/0 cable from the new meter/switch panel to the new breaker panel. My county requires NEC2005 codes, where and how do I ground this system to code? Does all of the grounding take place from the new meter/switch panel or am I required to also ground the main lug panel? Does it matter which hot runs to which bus bar? Or whether I locate the neutrals on the left and the grounds on the right?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 31, 2008, 02:00 PM
    Your grounding electrode conductors AND water bond/electrode conductors all go to the main disconnect.
    You will need a #4cu to the water pipe and connect within 5' of where the pipe enters. You must also jump around any meters or plastic fittings such as filters.
    You also need at least one ground rod to supplement the water pipe electrode. The wire to this can be a #6cu and should go from the disconnect right to the ground rod(s). Some areas accept one ground rod, some require the 25 ohm test and will simply require a second rod installed. You are NOT required to install any more than two rods.

    You DO NOT have to run four 4/0AL wires to the panel. You can reduce the neutral to a 2/0AL and ground does not need to be any bigger than #6cu or #4al.
    You can use anything larger if you desire, but the sizes mentioned are code.
    There's NO way I'd personally run FOUR 4/0al if I didn't have to.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

Upgrading from 100amp service to 200 amp service [ 1 Answers ]

I have a 1994 model double wide home, and would like to change my 100 amp service to 200 amp service. ( I want to go to electric heat) I have a disconnect at the house after the meter and it say 200amp. Is the wiring from there to my breaker box able to handle 200 amp service, and if not how do I...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

Upgrading to 200 amp with connection issues [ 11 Answers ]

Aloha Friends, I am renovating our newly purchased home. We have a meter main with the shutoff in our detached garage that runs underground with 2-0 aluminum to feed our 100 amp panel. We are bringing in the following electrical load: • five A/C's all 110 volt (five AFCI protected 20 amp...

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search