Drain/Vent Plumbing
I actually have two questions. I'm adding a bar sink drain to an existing laundry sink drain. The drain from the laundry sink is 1-1/2" PVC, and this goes to a sanitary double wye with 2" PVC going into the floor, and 1-1/2" PVC going up to a vent. I replaced a single sanitary wye fitting with the double wye. The bar sink will have an 8' horizontal run of 1-1/2" PVC with three 90 degree bends.
My questions are:
1. Is there a minimum bend radius for the 1-1/2" PVC 90 degree drain elbows? The local Home Depot has an overwhelming selection of various PVC fittings, and I don't know the difference between them. Some are marked ELL (should that mean something to me?), and I'm sure the others are marked as something else that I didn't notice.
2. I think I need a vent in parallel with the bar sink drain. If I connect the bar sink end of the vent with a tee within 3-1/2' of the bar sink trap, how high must the horizontal section of the vent pipe be above the sink or drain? Can it be connected to the existing vertical vent pipe with a simple tee, or do I need some other wye fitting? Is 1-1/2" PVC adequate?
|
|
 |
Uber Member
|
|
Apr 29, 2004, 08:28 PM
|
|
Re: Drain/Vent Plumbing
1 The longer the radius, the less likely anything will ever get stuck in it, and the faster the water will flow. Use the longest one you have room for. I haven't paid enough attention to be sure what the ones marked ell are. Are they also marked DVW? If not, they may be very short radius elbows meant for supply pipes. They will make poor drain elbows. Also, it may indicate they are a true 90 degrees. Drain elbows are slightly more then 90 to go from a true vertical to slightly sloping horizontal.
2 If Tom disagrees, go with what he says. I don't think you need a separate vent for each sink. You do need a separate trap for each sink to keep drain smells in the drain. PVC is a very forgiving material. It is my first choice for most uses. If you put it together without a vent, and have problems, you can always chop it open and glue in a tee to a vent. If you make the horizontal above the top of the sink, water can never run up it.
|
|
 |
Eternal Plumber
|
|
Apr 30, 2004, 05:33 AM
|
|
Re: Drain/Vent Plumbing
Hi Mike, (1)90 degree elbos come in a variety of flavors. Regular for water supply, DWV for drainage, a short sweep and a long sweep. Drainage does not like elbos that have short radius as they have a tendency to develop clogs. Go with DWV or a larger radius sweep if there is room.
(2) If code allows, 1 1/2" is acceptable, However we mostly use 2" in the walls and stubouts reducing to a 1 1/2" trap for bar sinks and lavatorys. To answer your question about venting your bar sink I would need more information about the vent you're reventing back into. If a major fixtures , (such as a bathroom group) discharge into the stack from above then you will need to revent back. I'm a little confused here. In one paragraph you say the bar sink drainage will be 8' long with three 90's and down below you tell me 3 1/2' from the trap to the vent. Which one is correct? Code states that the distance between trap and vent shall be 3 1/2' for 1 1/2" and 5' for 2" without having to install a individual vent. If you have to revent, you will have to connect the new vent to the one you're connecting to at least 2 inches above the flood rim of the highest fixture. The revent will tie into the old vent with a inverted drainage tee. (just turn it upside down) more questions? Click on back. Cheers, Tom
|
|
 |
New Member
|
|
Apr 30, 2004, 04:43 PM
|
|
Drain/Vent Plumbing
Wow. I appreciate your quick response. From both of you.
I guess I wasn't clear on the bar sink drain. From the trap it runs about 3' to a 90 degree elbow, and just past the elbow is the easiest place to put in a vent if it is needed. The drain then runs about 5 feet along a wall to the existing 2" drain into the floor. I need two 90 degree elbows to get the drain to line up with the double wye fitting. Nothing drains from above, but the laundry sink enters on the other side of the same fitting. The laundry sink drain is within a couple feet, so no vent is needed.
Is a vent required for the bar sink? It's the 8' horizontal run from the trap to the vertical drain/vent that I'm questioning. To comply with the code I think I need a vent just past the first 90 degree elbow. Am I interpreting the code correctly?
I sure appreciate your help. I had no idea plumbing was this involved.
|
|
 |
Eternal Plumber
|
|
Apr 30, 2004, 05:48 PM
|
|
Re: Drain/Vent Plumbing
Yor are correct. You will have to vent your bar sink within 3 1/2' from the trap to the new vent if the drain line is 1 1/2". Cut in a 1 1/2" drainage tee, point it up and connect the new vent to the existing vent at least 2 inches above the flood rim of the highest fixture or you could run it through the roof. The revent will tie into the old vent with a inverted drainage tee. (just turn it upside down). Sounds like you have it pretty well together. Good luck, Tom
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Kitchen sink plumbing/vent problem
[ 6 Answers ]
good morning to all!
I have a question that I hope someone can answer.I have an older modular home that we've decided to upgrade the kitchen in.I'm installing new cabinets and a new sink and also have decided to add a dishwasher next to the sink base cabinet.my problem is that the vent that goes...
Plumbing vent stack requirements
[ 2 Answers ]
I am re-doing a master bathroom. Currently there are (2) separate vent stacks in the upstairs, for two separate bathrooms. One stack from each bathroom. Can I elimiate one of the vent stacks and simply tie into the other and have (1) vent stack servicing both bathrooms.
The master bath had...
Plumbing vent to roof
[ 1 Answers ]
While trying to run a snake down the roof vent, the darn thing came completely out of the spindle and the snake fell down the vent. Now I have 14' of snake down the darn vent and can't see the free end. Is there some obvious tool I can find or rent that will allow me to fish the thing out?
...
Drain replacement/vent
[ 7 Answers ]
I searched around and couldn't find my answer.
I am renovating the bathrooom in my 1944 home. The house has had many "patches" to it in the past before I moved in. Because of the drain configuration now, I need to replace the pipe to the main drain. My question is that the tub is a good 10 ft...
Drain to vent pipe
[ 6 Answers ]
Hi I want to add a small sink next to my toilet, it is a cement slab floor, can I drain the sink into the vent stack of the toilet. A trap will be used for the sink. I really want to stay away from busting up the floor.
View more questions
Search
|