    Neutral wire used as a ground?
    I have been changing switches and plugs and in one of the receptical boxes I found the neutral wire pigtailed to the side of the box, and when I installed the new receptical there was no circuit until I did the same, pigtailed to the box... is this safe?:confused:
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #2

    Mar 26, 2008, 04:46 AM
    Quote Originally Posted by artosie
    I have been changing switches and plugs and in one of the receptical boxes I found the neutral wire pigtailed to the side of the box, and when I installed the new receptical there was no circuit until I did the same, pigtailed to the box... is this safe?:confused:
    No, it is not.
    The neutral should NEVER be connected to any housing or used as earth, simply because it is not earth.
    The neutral can have any voltage around 0 volt, depending on the load on the used transformer in your supply line.
    Disconnect a neutral line from housing, and use a connection block for interwiring.
    Sometimes a wrong wire colour is used for earth or neutral wire. Earth should always be green or green/yellow. Neutral should be blue (3 phase Eur) or white (2 phase US).
    .
    If necessary draw in another wire. If you do I advice you to draw besides the new wire also an extra wire (the last one to draw in whatever you need next time). Always handy!
    I am a qualified electrical contractor (in Europe - not in the US).
    ;)
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Mar 26, 2008, 06:42 AM
    Check the boxes(switch, receptacle or light)closest to the bad one and see if disconnected their, could even be bad or burned at panel also.
    Credendovidis, In the US, the System is actually Called "(Single Phase).
    As it is One phase, with neutral in the center. Take Care, Keep up the good work.
    artosie's Avatar
    artosie Posts: 5, Reputation: 1
    New Member
     
    #4

    Mar 26, 2008, 06:48 AM
    Excellent... I will check the other boxes near it.. it is an old building and running another wire is close to out of the question. I might have to cap the lines and put a steel plate over the box.

    Thanks for the quick and informative information! You are a great help

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Neutral / Ground [ 3 Answers ]

OK Strat, Here is the photo clip of the schematic of the Neutral /Grounding system in my place. Don

Is it okay to use bare wire as neutral? Okay to share ground? [ 53 Answers ]

Our house was built in 2003 and it came with a GE 24" microwave oven that uses 120 volts/20 Amp. The microwave stops working so we went out and bought a KitchenAid convection microwave oven that requires 20 Amp, 240 volts, 60 Hertz. The old microwave oven uses 12/2 w/g romex from a subpanel. ...

Neutral wire is hot(has voltage potential like the black wire) [ 5 Answers ]

Hi, The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...

Using Neutral as a Ground ? [ 3 Answers ]

In my new apartment there are some wall outlets that are two prong outlets. Also my fear is that the three prong outlets are not “physically” connected to ground. I heard somewhere that in this kind of system the neutral wire can also be used as a ground. Is this correct? Would a separate...


View more questions Search