Adding a nuetral bus to an old main panel
Greetings...
Can I add a neutral bus to my houses main panel... I have one bus in there now that is for both nuetral and ground... when I go to hookup the neutral from my 220 gfci breaker to that bus I keep tripping the breaker... the spa is a 3 wire 2 hots and a ground... the instructions say to hook up the neutral from the breaker to the neutral bus the diagram shows a separate bus for the neutral and one for the ground. Any suggestions... Thanks Joe
|
|
 |
Uber Member
|
|
Mar 22, 2008, 05:03 PM
|
|
The wire that says "load neutral" just cap and don't use because you don't have one.
|
|
 |
Electrical & Lighting Expert
|
|
Mar 22, 2008, 05:17 PM
|
|
You MUST connect that wire to the neutral/ground bar. 50A GFCBs don't have a "load" wire. They have a load terminal, which in your case will remain unused.
In a main panel the neutral and ground bar is the SAME. This is correct. You can add ground bar but NOT another neutral bar.
If you are tripping the breaker simply by connecting the white from the breaker to the neutral/ground bar then you have a mis-wire somewhere.
Where did you connect the ground (on both ends)?
|
|
 |
New Member
|
|
Mar 22, 2008, 08:21 PM
|
|
You might not have connected the white wire from your cable feeding the circuit to the breaker, then the breaker white to the neutral bar. A GFCI breaker will have both the white and black connected to it. The breaker needs to monitor the current leaving the black and returning on the white, If it's not he same it will trip out. So both the white and black are connected to the proper terminals on the GFCI breaker.
|
|
 |
Electrical & Lighting Expert
|
|
Mar 23, 2008, 04:50 AM
|
|
 Originally Posted by contractor
You might not have connected the white wire from your cable feeding the circuit to the breaker, then the breaker white to the neutral bar. A GFCI breaker will have both the white and black connected to it. the breaker needs to monitor the current leaving the black and returning on the white, If it's not he same it will trip out. So both the white and black are connected to the proper terminals on the GFCI breaker.
Just so we are clear. This is a 240v, two-pole, GFI breaker. There are two hots and NO neutral in the circuit in question. It is a straight 240v circuit.
|
|
 |
New Member
|
|
Mar 23, 2008, 06:29 AM
|
|
 Originally Posted by stanfortyman
Just so we are clear. This is a 240v, two-pole, GFI breaker. There are two hots and NO neutral in the circuit in question. It is a straight 240v circuit.
That's correct, I missed the 50Amp 2 pole.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Ground/Neutral Bus in Main Service Panel - Is there a Difference?
[ 8 Answers ]
I'm preparing to provide new wiring to a sizable addition to a log home. Prior to beginning the new work I mapped my existing circuits thinking it best to correct any potential overloads in the existing panel/circuit design before introducing any new problems on my own.
Decided to make a few...
Breaker size in main panel to support sub panel?
[ 7 Answers ]
Hello,
I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel.
TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC
...
Adding main electric panel in multi-family house
[ 1 Answers ]
Hello,
I just but a two-family (two levels) house in Gibbstown, NJ. The house only has one main circuit breaker panel feeding both apartments. My plan is to live in one unit and rent the other unit. Currently the house only has one electric power meter and one circuit breaker box. The meter...
Why is the grounding and neutral bus bar connected in the sub panel?
[ 1 Answers ]
I had an electrician come in and install a new sub panel in my house and wire up my kitchen. When he finished, I took it from there. Now that I have the rest of the house wired, its time to connect it all to the sub panel. Both the neutral bus bar and the ground bus bar (2 separate buses) seem to...
View more questions
Search
|