    Difference between 110 V and 220 volt rating cable
    In usa domestic voltage is 110 volt whereas in britain and asia we use 220 volt. I was asked that whether can we use american cable for 220 volts supply. I know the current carrying capacity is based on the cross sectional area of the conductor and insulation thickness. In usa AWG is used whereas in britain,asia etc we specify the cable according to cross sectional area. My question is whether the insulation thickness for 110 V and 220 V cable will be same for same cross sectional area. Can somebody provide specifications for 110 v cable.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Feb 8, 2008, 12:06 PM
    Cross sectional area of the wire has no bearing. Most portable cable in the US is either 300 V or 600 V. Unfortunately even the manufactures fail to mention rms, DC or p-p in their notation.

    It seems to be an rms value when I questioned a manufacturer once.

    Insulation is material and thickness dependent. Ratings also have a safety factor built in. Teflon, for instance is 1000v per 0.001"

    Typical building wire used in the US is NM-B. Generic specs here: Tractor Supply Company - Romex 12-2 CU NM-B Wire Gauge 25 ft
    msk's Avatar
    msk Posts: 59, Reputation: 3
    Junior Member
     
    #3

    Feb 8, 2008, 12:33 PM
    Thank You for the reply
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Feb 8, 2008, 12:43 PM
    I edited my response to say "cross sectional area of the wire has no bearing"
    danar's Avatar
    danar Posts: 69, Reputation: 2
    Junior Member
     
    #5

    Feb 25, 2008, 10:13 PM
    In addition if we talk of volatage rating of a cable it refers the insulation.. but if we talk about the cross sectional area it refers to its ampacity..
    steelatkite's Avatar
    steelatkite Posts: 2, Reputation: 1
    New Member
     
    #6

    Feb 26, 2008, 12:54 PM
    The cable of 220v is large in diameter and cable of 110 volt is small in diameter then 220v cable.
    danar's Avatar
    danar Posts: 69, Reputation: 2
    Junior Member
     
    #7

    Mar 9, 2008, 02:05 AM
    Usually low voltage cables are rated up to 1000v.. so there is no question whether you use it in 110v or 220v
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #8

    Mar 10, 2008, 06:53 AM
    danar:
    Try again. 300 and 600 Volt cables are very common. SHow me a 1000 V cable.
    danar's Avatar
    danar Posts: 69, Reputation: 2
    Junior Member
     
    #9

    Mar 11, 2008, 03:08 AM
    As per your NEC




    As per NEC tabel on Allowable Ampacities of single insulated conductor from size 2.0mmsq up to 500mmsq these conductors are rated FRom 0 to 2000V.. please refer to your NEC tables...
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #10

    Mar 11, 2008, 12:08 PM
    Based on the original post, I assumed that the reference was for portable cable rather than building wire. Who knows, we both could be wrong.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

110 volt versus 220 volt mini heat pump [ 6 Answers ]

I have enclosed my screened porch to create more living space(Florida Room). I am using a single zone mini split ductless heat pump for heating and cooling. It has been calculated that I need a 12,000 BTU unit. However, most of these units are available in 110 volts and 220 volts. The 220 models...

Assemble a 220 volt outlet from two 110 volt circuits [ 5 Answers ]

I need help making a temporary 220 volt outlet cord. I have the female 220 v receptacle and two extension cords. I need this to connect a window AC. The electrician cannot come until mid next week. It is very hot here. He told me to put one these cords together for a temporary fix. He warned...

Switching from a 110 volt to 24 volt thermostat [ 5 Answers ]

I have a 1950's era hot water boiler using the baseboard style radiator. There is only one zone in the entire home. I would like to switch to a programmable style thermostat to better manage the heating in the house. Is there a way I can switch to a 24 volt thermostat using a relay or switch? ...

110 volts to 220 volt [ 5 Answers ]

How can I change 110 volts AC to 220 volts AC


View more questions Search