    Goodman vent motor
    I have a gmnt 80-4b furnace that stopped running. The vent motor is not getting any power. I have power at both sides of the high limit switch, power to the flame sensor, and power to one side of the pressure switch. Anybody know why I am not getting power to the vent motor?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Feb 22, 2008, 07:40 PM
    Make sure you have 24v on the W circuit. You may have a bad thermostat or broke thermostat wire. Jump from R to W to see it it will start working.
    rsbny's Avatar
    rsbny Posts: 6, Reputation: 1
    New Member
     
    #3

    Feb 22, 2008, 07:54 PM
    The thermostat is working and calling for heat. I have power at the W terminal, but the venter doesn't respond to the call. I have replaced the control board wire for wire, and have also replaced the pressure switch and still no luck.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Feb 22, 2008, 08:08 PM
    If you have an open vent limit switch or rollout limit switch it will keep the inducer motor from running. The two are manual reset limits(small button in the center of the limit switch)Locations: rollout limit just above the burners, vent limit on the vent pipe just above the inducer motor inside the furnace.
    rsbny's Avatar
    rsbny Posts: 6, Reputation: 1
    New Member
     
    #5

    Feb 22, 2008, 10:27 PM
    The rollout switches are not tripped and I see no sensor on the vent pipe. I am not sure if a draft inducer is the same as a venter or if there is a difference based upon the furnace efficiency, but my furnace is vented with pvc pipe and there are no sensors on the vent pipe. The limit switch I found on my furnace does not have a reset, but I jumped it out and it made no difference.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #6

    Feb 23, 2008, 09:36 PM
    You should have a diagnostic light telling you what's wrong.
    rsbny's Avatar
    rsbny Posts: 6, Reputation: 1
    New Member
     
    #7

    Feb 24, 2008, 06:22 AM
    3 blinks--either bad pressure switch, blocked vent, or bad venter. I have checked all these possibilities already. I have manually opened and closed the pressure switch with no results, and checked for blockages. The problem is the venter doesn't even try to start because it gets no power.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 24, 2008, 07:18 AM
    Check the switch on the venter motor itself if it has one. There should be power wires going to the vent motor and switch wires if your goodman is so equipped.

    Also did you check the pressure switch contacts for continuity (open and close) with a meter if so equipped when you manually tested it?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #9

    Feb 24, 2008, 06:32 PM
    If you do not have 120v going to the inducer motor(venter motor) after you reset the control board by turning the power off for a few seconds and then back on with your thermostat calling for heat I would say you have a bad control board or bad inducer relay. Depends on if your motor wires go to the control board or relay.
    rsbny's Avatar
    rsbny Posts: 6, Reputation: 1
    New Member
     
    #10

    Feb 24, 2008, 07:24 PM
    The motor wires go to the control board and I have already changed the board out with no luck. Do you know anything about the integrated fan/ignition control that the manual says is located in the air blower compartment? It says it is not field serviceable and I am wondering if this may be my problem.
    darress's Avatar
    darress Posts: 1, Reputation: 1
    New Member
     
    #11

    Feb 25, 2008, 09:04 AM
    I also have a Janitrol/Goodman furnace model GMP100-4 with similar problems. After trouble shooting the pressure switch and cleaning everything out (there was no blockage by the way) I'm finding that my issue is the venter motor itself. It gets power after power-off reset and closing door switch, but the motor does not respond. I get a high pitch humming from the control board area as well. I'm trying to locate a new venter motor now. It looks like I have to buy the whole venter assembly as a replacement, housing and all. It sounds like you don't have power to the motor in your case, but did you try turning off the power for a minute or two to let everything reset and then test for power to the motor?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #12

    Feb 25, 2008, 12:03 PM
    If you will supply a accurate model number I will try to locate your furnace and take a look.
    rsbny's Avatar
    rsbny Posts: 6, Reputation: 1
    New Member
     
    #13

    Feb 25, 2008, 02:27 PM
    I have finally figured out the problem. The second control board I installed was also bad. I tried a third board and it fired right up. Thanks to everybody for your input.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman Inducer Motor [ 18 Answers ]

I have a Goodman Gas Furnace installed in 1997 and have been experiencing the following problems: The usual run for the furnace has been inducer motor on, ignition (with flames), and then the blower motor comes on. I have been having the inducer motor come on, run for about three minutes,...

Blower motor wiring on a Goodman GMP [ 2 Answers ]

I have a Goodman GMP forced air furnace running on natural gas. It is about 5 - 6 years old. It recently went out. The draft inducer would come on and the igniter would glow but then it would shut down without opening the gas valve. I checked and found that the board was never sending a...

Goodman blower Motor [ 1 Answers ]

Where can I find a blower motor for a Goodman gas furnace?

Goodman furnace induced draft motor [ 3 Answers ]

On a call for heat the draft motor starts but the air proving switch does not close. I replaced it with the same result. Everything works normally if I close the switch manually with my own air pressure. Someone told me that somethimes the motor, due to age (this one is 13 years) will not spin fast...

Goodman furnace fires up, but no blow.(new motor) [ 1 Answers ]

The furnace fires up for a few minutes but the blower motor doesn't engage. Then the safety switch kicks in and turns the flames off. You can hear the click of the relay and the low moan of the motor trying to go. Sometimes it'll click on.. you hear the motor strain... then click off, then click...


View more questions Search