    Running power to a cabin in the country
    I have a distance of about 250 feet that I want to put electricity to a building from my existing meter pole. I would like to know what size wire to put in the ground.

    Use: a few small cabins (12'x16', 12'x12', and another 12'x12'). The cabins will have a window unit A/C, a small refrigerator, and possibly run an air compressor or some power tools once in a while.

    The service is about 250 feet away from the pole. I plan on burying the cable. I also have to run through a small creek (not usually wet). 100amp meter pole (already there).

    What do you recommend?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 31, 2008, 02:54 PM
    You can use aluminum wire rated for direct burial, called URD (Underground Residential Distribution) cable.

    This comes in 3 and 4 wire, if the main breaker is at the meter, then use 4 wire, if the main breaker is at the cabin, then only 3 wire is needed.

    Assuming a 50 amp load, #1/0 Al will get you a 3.2 % voltage drop. If you can afford it, esp if you plan to add more load later, then I really recommend using #4/0 Al URD cable. This will allow 100 amps of load at 3.6% Vd.
    ltwayne's Avatar
    ltwayne Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 31, 2008, 04:12 PM
    Please forgive my ignorance, but I would also like to understand more about what you are suggesting...
    I have heard of direct burial cable, but I am not sure if the cost of 250 feet will be really significant or not. I priced THHN and for number to the electric company quoted $1.28 per foot. I also priced Direct Burial (3 number 2's with a ground) it was about $5.93 per foot. Does that sound about average? Number 4 was $.81 and $4.15 respectively.
    Is there a difference in "Number 4" and "#4/0"? (again, please forgive my ignorance... that is why I am here at the site for advice)
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 31, 2008, 05:21 PM
    All your prices seem reasonable, I am assuming the #2 THHN is copper, and that the direct burial is aluminum.


    Forget THHN, that is for dry locations only, not allowed in wet locations, which would be a conduit underground.

    Most THHN is also rated THWN which can be used in underground conduit. THHN/THWN must always be in a conduit, never direct buried.

    The smaller the number the larger the wire, #12, #10, #8, #6, #4, #3, #2, #1, #1/0, #2/0, #3/0, #4/0. The "0" stops there, and starts with the actual circular mils called MCM. Ok enough on wire sizes.

    If you use #2 copper, there will be a 3.2% Vd with a 40 amp 120 volt load.

    If you use #2 aluminum, there will be a 4.5% Vd with a 40 amp 120 volt load.

    I should explain that the maximum recommended voltage drop is 3% for a feeder, and 2% for a branch circuit to the last outlet.

    With the AC and motors you mention, really need to keep the Vd as close to or below 3% as much as practical.
    ltwayne's Avatar
    ltwayne Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 20, 2008, 09:53 AM
    I have talked to several people here locally (friends, not electricians). They are mostly telling me to stay away from aluminum (because of corrosion and heat). The cost is about 75% less for aluminum. Should I stay away? What are your thoughts?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Feb 20, 2008, 10:05 AM
    FYI #4/0 is the same as 0000. Just like purity numbers of 5N5 is 99.9995% pure, but that another area all together. It's just shorthand.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Feb 20, 2008, 05:41 PM
    Kiss, sounds like 5N5 is purer than Tripple Nine Fine?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #8

    Feb 20, 2008, 07:12 PM
    See, I'm not making it up.

    Virtual Travelog | 5 Nines and other Nonsense - Interaction of Quality Attributes in System Design

    Type as a Google search "5N5 purity"
    Mr_am's Avatar
    Mr_am Posts: 105, Reputation: 4
    Junior Member
     
    #9

    Feb 22, 2008, 06:34 PM
    Hi, Aluminum is less reliable (cheaper).. copper is the best.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ceiling Fan w/power off won't stop running! [ 7 Answers ]

After installing my Hampton Bay Fan, everything was normal. Several weeks later, the fan began to intermittently run backwards at 6 RPM (very slow) when both the fan motor switch and the light switch, (both are wall switches) ARE TURNED OFF!! It then stopped this behavior. Now, several months...

Running power to a detached workshop [ 1 Answers ]

With apologies for what might be a stupid question. I'm thinking or running power to my workshop (40 feet) and busy reading up on what is involved... I plan on doing the job myself as I'm a reasonably experienced handyman. I'm told I should run something like 8/3 2 feet underground although not...

Maytag side-by-side refrigerator low cabin cold upper cabin warm [ 1 Answers ]

I have a maytag side-by-side refrigerator. I noticed that in the refrigerator section the low part ( where there is an air duct opening to the freezer). However, the upper part is warm. I have tried changing the temperature control it doesn't seem to be helping. Apparently the freezer is...

AC/Heating unit stopped running - No power [ 4 Answers ]

My Janitrol AC Heating unit stopped running suddenly. I can neither use the Cool nor Heat (if I switch to either on the thurmostat I hear nothing). The fan doesn't run either when switched to ON. I checked the cirtcuit braker for the AC/Heating using and it was in the ON position, but when I try...


View more questions Search