    Do I need derate my wires from basement to attic ?
    I have a 200A service panel main in the basement. I'll be installing a subpanel
    Main lug in the attic with a dual pole 60A breaker in the basement main feeding this
    Attic new subpanel. Using a #6/3 romex wire from basement to attic
    (about 35 - 40 feet total wire length).

    Along with this #6/3 romex wire (from basement to attic), I'll be bringing 2 more 14/2 romax wire from a couple of HOT switches (HOT goes to switch first) located in the lower
    Levels, to the attic to control a copule of sets of flood lights (150W for each set).
    These flood lights are installed outside of the house to light the front and back yard.

    Question:
    1. Since I have 3 wires at long lengths,
    #6/3 romex at 40' on a 2pole 60A breaker
    #14/2 romex at 50' on a 15A breaker
    #14/2 romex at 60' on the same very 15A breaker
    Coming from basements to attic, do I need to derate my wires?

    2. I Would appreciate it greatly, if someone explain in details,
    In what conditions one needs to derate, and what does derating really do ?
    e.g. is it voltage drop a concern that derating addresses,
    Is it wire over heating conditions that derating addresses, etc.
    Thanks in advance
    -Ab
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 13, 2008, 08:45 AM
    Derating is related to the quantity of current carrying conductors bundled, such as when individual wires are pulled into a conduit.

    When 4 or more current carrying conductors, and I keep saying that because in most cases the neutral is current carrying, derating is necessary to minimize the load on these wires in an effort to keep the heat created minimized.

    Cables only need to be derated if they are bundled, such as tyrapped into a bundle. I do not believe this is your case, and derating is not necessary in your situation.

    Derating is done by either of two methods. Either redcue the size circuit breaker, if applicable, or mostly, by increasing the size.

    I am going to stop here, as there are several more details that will get lengthy to explain, having to do with the ampactiy rating of a certain wire at a certain temp ratng.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement ceiling exposed duct, pipes and wires [ 1 Answers ]

My basement ceiling to floor measue 72" from floor to drywalled ceiling. My problem the prior owners attached ductwork and wires over the drywall. A suspended ceiling will not work takes up too much height. Walls and floor concrete. Any suggestions would be helpful. If I could see some...

3 wires + 2 wires  POOL MOTOR [ 2 Answers ]

I need help connecting a motor for my pool. The motor has 3 wires coming out of it. 1 white, 1 black, 1 black with a white stripe. A continuity test on the 2 blacks says they are wired together somewhere. I have a power cable coming out of the ground. 1 white + 1 black cables inside. ...

Thermostat Wires - Only 2 Wires (both black) [ 4 Answers ]

Hi there, I'm switching my thermostat for a newer digital one, though when I took out the old thermostat, there were only 2 black wires with white stripes on them. The new thermostat calls for an RH wire and a W wire, but I have no way of distinguishing the two apart. How can I tell which wire...

Attic plumbing [ 3 Answers ]

Hello, Im looking for info on adding a complete bathroom to my attic, my question Is really about the drains, I want to ad a shower, tiolet, sink. There is a bathroom almost directly (about 3ft over ) below where I would like to put this. I was wondering if I can connect to the drains...

Hampton Bay remote wires do not match fan wires [ 1 Answers ]

Yesterday I installed a new Hunter ceiling fan. I also purchased a Hampton Bay wireless wall switch. Everything went well until I wired up the remote receiver. The receiver has a blue wire for the light that is supposed to connect to the blue wire (light) from the fan. The Hunter fan does not have...


View more questions Search