New Member
|
|
Feb 10, 2008, 06:40 PM
|
|
Detached garage sub-panel
First I want to thank those who have given such good advice on this forum.
I have a 900sqft detached garage. I am installing a 125amp sub-panel. I plan to install a 100amp main in this panel.
The house is 100ft away. My plan is to run 2" PVC sched 80 conduit from the house to the garage. I will burry it 24" deep. I will install 2 ground rods 6 ft. apart near the garage main, and run #4 copper from the rods to the ground bar in the new panel. The neutral and ground in the sub-panel will be isolated (no bonding screw)
I will run 4 wires from the house. Three #2 copper, and one #6 copper. The breaker in the house will be 100 amp as well.
My question is, do I have the wire size correct? If I were to run aluminum to save money, what size aluminum would be appropriate. Also what type of wire do I use. I've heard several different acronyms but not sure which one is correct for this underground application.
Also, if you can think of anything I should change... thanks!
|
|
 |
Uber Member
|
|
Feb 11, 2008, 06:11 AM
|
|
#4 is allowed for a residential 100 amp feeder. The #2 you propose is fine as it helps greatly with voltage drop. With an 80 amp load, the Vd will be 2.43%.
To do voltage drop calculations, the amp load must be used. Assuming a 50 amp load, #2 aluminum will give a 2.45% Vd, the max recommended is 3% for a feeder.
If the load will be any greater, then you may want to consider using #1 Al.
Assuming the conduit will be a complete system, with fittings, from point to point, then you may use aluminum wire with XHHW insulation.
You can find copper wire in THHN/THWN, only for conduit, and XHHW, which also is only for conduit.
The acronyms you may have heard are USE and URD. USE is an insulation on individual wires that can be direct buried in earth. URD is Underground Residential Distribution, can be three or four wires twisted into a cable assembly, can be direct buried in earth.
|
|
 |
New Member
|
|
Feb 11, 2008, 09:50 AM
|
|
[QUOTE=tkrussell]#4 is allowed for a residential 100 amp feeder. The #2 you propose is fine as it helps greatly with voltage drop. With an 80 amp load, the Vd will be 2.43%.
The load will likely be closer to 80 than 50. I haven't done a load calculation yet, but some of the constants are big, like the water heater for radiant heat, dust collection, air compressor, air filtration system, plus the saws, and welder. So it sounds like I should use either #2 copper or #1 AL. I will do a load calculation first, and then a Vd.
You can find copper wire in THHN/THWN, only for conduit, and XHHW, which also is only for conduit.
What are the differences between THHN and XHHW? Any advantage to using one over the other?
|
|
 |
Uber Member
|
|
Feb 11, 2008, 11:07 AM
|
|
Most THHN is dual rated THWN. THHN is for dry locations, THWN is allowed in wet locations, ie: an underground conduit is considered as a wet location.
XHHW is wet location rated. It actually is a fraction smaller in diameter than THHN/THWN.
While THHN is used the most, I find that THHN has a layer of material that will wrinkle and bind at times. XHHW is very smooth and slick.
Either thou can be used in a buried conduit. Compare prices if available.
|
|
 |
New Member
|
|
Feb 12, 2008, 06:33 PM
|
|
Thanks for the great information!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Ideal Amps for detached garage
[ 2 Answers ]
Hi, I am planning to build a detached garage with electrical which is about 24' from the house main panel. I plan to have about 6 outlets and one with the 220V for the washer\dryer in the garage. What will be a ideal Amps to support these? Thanks in advance,
Adding a new toiletshower in a detached garage
[ 5 Answers ]
Hello, I am new to the forum and have enjoyed reading all the valuable knowledge people sharing here. I am planning to build a detached garage about 24' from the house and about 35' to the vertical drainage pipe locates in the bottom of the tri-level in which is about 5' deep from the surface. I...
Detached garage pad
[ 2 Answers ]
I am trying to get some information on building a garage starting with the Pad. I am planning on building a 22X26 detached garage. The rough grade was completed about 4 months ago. It is a clay base with no topsoil added yet. Should I get a bobcat in to remove a couple inches or just pack down...
Detached garage grounding rod or not
[ 1 Answers ]
Hi, I just ran across another problem. I will be running 40 amps 240 volts out to my garage via underground 8-3 plus ground. Do I need a grounding rod at the garage or is the ground via the service cable to the garage enough? I have seen both and am not sure why. Is the 240 volt service to the...
Detached garage panel install, please help
[ 2 Answers ]
Hi, I am running 8-3 underground in pvc conduit and am wondering:
1. How high up the garage wall I should come up before entering the garage (I guess this means how high the panel will be on the inside as well)? Any code for this or is whatever height is comfortable good enough?
2. Also, I...
View more questions
Search
|