    Two electric baseboard heaters on the same circuit
    I’ve installed two electric baseboard heaters on the same circuit but I did no daisy-chain them. Instead I have my 12/2 coming from the powerbox (220 v - 20 amp breaker) to the thermostat and splitting in a ( Y ) with a set of wires going to baseboard A (1500 W) and a set going to baseboard B (750 W).

    Is this ok… Everything works but for some reason the thermostat is kind of warm.

    Thanks
    bolt in blue's Avatar
    bolt in blue Posts: 68, Reputation: 2
    Junior Member
     
    #2

    Feb 6, 2008, 09:45 AM
    I'd check the rating on the thermostat. It's possible that your thermostat is rated for a smaller load than the 2250 W you have connected. You'll need a thermostat rated for at least 9.4 amps since you have 240 volt heaters.
    Marioriggs's Avatar
    Marioriggs Posts: 4, Reputation: 1
    New Member
     
    #3

    Feb 6, 2008, 10:51 AM
    Actually the electronic thermostat has a capacity of 240 v / 12.5 amp / 3000 w.

    I use the same thermostats all over the house and some with 2500 w heaters. No such problems.

    What worries me the most it the fact that I put a junction (split) between the thermostat and the baseboards instead of daisy chaining them.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Feb 6, 2008, 03:14 PM
    As long as you have the two cables feeding the heaters connected properly to the LOAD terminals of the stat, blacks on one and the whites on the other, you should be fine.

    The heaters you have should be drawing the 9.4 amps as mentioned by BIB, and that is below the amp rating of the stat, so that is fine.

    Daisy chaining the heaters would not affect the amp draw, both heaters would still draw the 9.4 amps.

    A "kinda warm" is subjective. I would keep an eye on the stat, as there may be a defect in it to cause heat. As long as it does not get too hot to touch, then it should run OK.

    If you have other stats of the same rating, try swapping this one with another, and see if the heat you feel is the same.

    Keep your receipts handy in the even these stats can't "take the heat", so to speak.
    Marioriggs's Avatar
    Marioriggs Posts: 4, Reputation: 1
    New Member
     
    #5

    Feb 6, 2008, 09:39 PM
    Here is what I did (everything is grounded)

    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Feb 7, 2008, 10:28 AM
    Wiring diagram looks good. I see no problems.

    Only issue is, as a safety precaution, with using a single pole stat, it cannot be used as a disconnect, as you can see, it only breaks one power leg to the heater. Must use the breaker as a disconnect.

    Otherwise there should be no problem.
    Marioriggs's Avatar
    Marioriggs Posts: 4, Reputation: 1
    New Member
     
    #7

    Feb 7, 2008, 11:31 AM
    http://www.broan.ca/PDF/Specifications/1T22d021023.pdf (this is not my thermostat)

    Besides the extra security are there any advantages of using a double pole thermostat?

    Actually I just found this :

    What is the difference between a double pole and a single pole thermostat?

    CHECK LOCAL CODES FOR BUILDING REQUIREMENTS

    Single pole thermostats break only one side of the power line to your heater and cannot be turned "off". Therefore, power is continuous to the heater even if it is not running. The control knob will have a low temperature setting without an "off" position.
    Double pole thermostats break both sides of the power line; therefore all power to the heater is interrupted. The control knob will have an "off" position.


    Is it better to turn off all the breakers related to heating when not it use (summer)? Besides the security issues, would this save electricity?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Feb 7, 2008, 11:56 AM
    A single pole stat opens one leg, the heater stops operating, no current is being used, so does not matter if the breakers are left on, no electric usage will occur, so no savings to be had.

    National code will allow the single pole stat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3 new electric baseboard heaters [ 12 Answers ]

We are trying to wire 3 baseboard heaters (all 240V: 750W, 1000W and 1500W, in parallel) attached to a douple pole 20amp breaker. We tried 12 gauge 2 wire first and they were working but not much heat. So someone told us maybe we'd only wired them using 120V(? ). So we now have re-wired them using...

Electric baseboard heaters [ 3 Answers ]

I have Federal Pacific electric baseboard heaters in my home. 2 out of the 4 baseboards on my first floor will not turn off. I replaced the thermostat with no luck.

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...

Electric baseboard heaters [ 1 Answers ]

What size wire and heatre do I need for a room size 15*11

Electric baseboard heaters [ 3 Answers ]

One of my electric baseboard heaters makes a high pitched hum when turned on to 70 degrees, unlike the others. What could be causing this and how can I fix it?


View more questions Search