How to size Conduit 6-3
I have 2 6-3 for a 60ft run and 1 6-3 for another run. Question, what size conduit do I use. This circuit is for a tankless water heater. All will in my garage which is drywalled.
|
|
 |
Uber Member
|
|
Feb 4, 2008, 06:04 AM
|
|
While there is a calculation to determine the size conduit for one cable, I would not recommend pulling any large cable through conduit for any great distance.
Since your using conduit, you should be sure the conduit system is complete with all necessary fittings from point to point, and pull in individual wires using THHN or XHHW insulation.
If you insist pulling #6-3 cable through conduit, give me the outside dimension of the cable, or better, the type and brand cable, I can find the manufacturer's spec sheet, from there I can do the conduit fill calcs.
Also, are you sure your existing service can handle the high amp load of these water heaters?
|
|
 |
New Member
|
|
Feb 4, 2008, 11:33 AM
|
|
 Originally Posted by tkrussell
While there is a calculation to determine the size conduit for one cable, I would not recommend pulling any large cable thru conduit for any great distance.
Since your using conduit, you should be sure the conduit system is complete with all necessary fittings from point to point, and pull in individual wires using THHN or XHHW insulation.
If you insist pulling #6-3 cable thru conduit, give me the outside dimension of the cable, or better, the type and brand cable, I can find the manufacturer's spec sheet, from there I can do the conduit fill calcs.
Also, are you sure your existing service can handle the high amp load of these water heaters?
I am Installing 2 Heaters in Parallel, this is supposed to be required for each Heater. Have a 200 amp service.
Wire is marked as follows:
E18679 (UL) Romex (R) SIMPULL (TM) awg 6 cu 2 cdr w/awg 10 grnd TYPE NM-B 600 volt 9/07/07
|
|
 |
Uber Member
|
|
Feb 4, 2008, 05:25 PM
|
|
You should have a flat cable, the larger dimension is .693", and one cable can fill up to 53% of a conduit, so you need 1-1/2" conduit.
You can staple or strap the cable to the upper parts, out of harms way, in the garage, suing short pieces of straight conduit as protection. Even fairly longs runs, as long as it is straight. Believe me, if you try to pull this through a conduit bend, you will have a great deal of problems.
|
|
 |
New Member
|
|
Feb 4, 2008, 05:41 PM
|
|
 Originally Posted by tkrussell
You should have a flat cable, the larger dimension is .693", and one cable can fill up to 53% of a conduit, so you need 1-1/2" conduit.
You can staple or strap the cable to the upper parts, out of harms way, in the garage, suing short pieces of straight conduit as protection. Even fairly longs runs, as long as it is straight. Believe me, if you try to pull this thru a conduit bend, you will have a great deal of problems.
Thank you very much for the input, I truly appreciate it.
Gene
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Queen size frame-full size mattress
[ 2 Answers ]
I have a full size mattress set and want to know if it can be used with a queen size bed frame? I heard there was a kit that can be used to make it fit.
Wire Size and panel size
[ 6 Answers ]
I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...
Proper wire and conduit size?
[ 2 Answers ]
Hi, I have just had a new pole building built. I had a 200 amp service installed. I will be installing 16 fluorescent light units. I will install them on at least 2, possibly 3 circuits. My question is what is the formula for figuring out the proper wire size, and how many of these conductors can I...
Do I need conduit?
[ 4 Answers ]
I have a panel in my garage for my garage based workshop.
I want to run a 220 volt circuit (have have the capacity in the panel to do so).
My question is whether I need to run the wire inside conduit or can I run romex without conduit.
The wire will be behind drywall the entire way so it will...
View more questions
Search
|