    Hello, I've read some of the posts on spa wiring and have a few questions about my project. I am wiring a 230V spa that is greater than 80 ft from the panel (approximately 130 ft). Because the spa normally requires 6 gauge, I assume 4 awg is appropriate for that distance so my plan is:

    50 ft 4/3 THHN in the house from 50 AMP breaker in the panel to junction box on the side of the house.
    80 ft 4/3 UF to GFCI 50 amp breaker within 6 ft of the tub, with an off switch mounted next to it.
    Metal conduit for the house and brief runs where the UF cable goes into and comes out of the ground.
    6 ft section of 6/3 from GFCI 50 amp breaker to the tub, with a metal conduit coming out of the cement where it connects to the tub

    1) How does this look?
    2) Will 50 amp breakers be capable of interfacing with 4 gauge?
    3) Should I use another type of 4/3 other than UF and run water tight conduit the whole distance?
    4) Where is the best place to buy 4/3 wire, I've had difficulty finding it online, is it best to go to a local supply place?
    Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 3, 2008, 07:11 AM
    My answers are in bold:

    1) How does this look?

    Your plan looks fine as outlined. The #4 will help with voltage drop, and is the correct choice for this distance. Keep the service switch away from the tub at least 5 feet.

    2) Will 50 amp breakers be capable of interfacing with 4 gauge?

    I believe the #4 will fit in the lugs on a 50 amp breaker. Check the specs or label on the breaker, the wire size range will be listed.


    3) Should I use another type of 4/3 other than UF and run water tight conduit the whole distance?

    Those are your only two choices, UF or conduit. Compare prices. Conduit will allow easy future repairs or upgrades.


    4) Where is the best place to buy 4/3 wire, I've had difficulty finding it online, is it best to go to a local supply place?

    An electrical supply distributor may be your only hope for this cable. Check to be sure the distributor sells to the public, many, such as Graybar, will only sell to contractors.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New Spa wiring [ 1 Answers ]

I am installing my new spa and it is set up as a 3 wire 240 VAC, 60Hz unit. My previous spa used 4 wires (red, black, white, and ground). The new one appears to use red, black, and ground. Can I use my old GFCI (made to use red, Black, White) on the new module and have it work properly without...

Spa GFCI wiring [ 0 Answers ]

Here is a visual. Full size it to read the print. Make sure to use correct wire size for load, distance and location conditions. Copper is not cheap, neither is safety it has a heaftier price. Find the name on hot tub "control pack", not hot tub "Brand" Some may only be three wire hook up...

SPA Wiring [ 3 Answers ]

I have run wires from my main box to the location where I wish to install my spa. I have 3 10 gauge wires (2 power, 1 common) all underground in conduit. Do I sink a rod in the ground for the ground or do I need to run another wire from the box? What are my options? I have also run wires to my...

GFI Wiring for spa [ 2 Answers ]

My friend is wiring a hot tub. He has a 40 AMP at the house and ran 8/3 from the house to the receptacle at the tub. He grounded the ground at the ground bar in the panel, and connected the like color wires directly to the tub at the recetacle box, 3 1/2 feet up from the floor. The GFI (a 50...

Spa wiring questions [ 4 Answers ]

I recently purchased a hot tub (spa). It calls for 6-3 with ground 240 volt 50 amp gfci breaker installed. I have almost completed the job and have some questions. I installed a 50 amp breaker in a subpanel in my laundry room and ran the 6-3 wire with ground down in the crawl space out to the...


View more questions Search