    Furnace Trips Fuse after a day/two
    Hi. I have split unit. With the Air handler / Furnace in the Attic. There are three Fuses. One by the condenser outside unit, one at the main CB, and one in the attic next to the Furnace. Two days ago the heater melted the attic service breaker, so the CB Box got replaced thinking it was a faulty box. Today it tripped the CB again. The fan and heat will run for a day or so, then it acts as if it is overdrawing Amps. I replaced the capacitor thinking it was the motor having a hard start. Could it be that the motor is just over drawing amps after it runs for while and gets hot?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 3, 2008, 12:58 AM
    The best way to find your problem is with a Amprobe. This way you can take current draw measurements and check them against the furnace/air handler manufacture plate. All power needs will be addressed on that plate and when you take a reading you just compar. Anything electrical that is using more current than on the manufacture plate should suspect of causing the problem.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My furnace blows the fuse [ 1 Answers ]

I have a Comfortmaker Furnace (approximately 1998/99) and the fan will not turn on allow the furnace to heat. When I try to turn the furnace on it blows a 3 amp fuse at the blower motor. I removed the fuse and jumped it and all it will do is make a faint buzzing noise and not turn on. I can see...

3A fuse blowing after furnace ignites [ 5 Answers ]

'Working on a 10-yr old Goodman GMP050-3. A/C is okay, but no heat. Circuit board and ignitor were just replaced and the flame sensor has been cleaned. The unit comes on, status light solid, ignitor glows, gas comes on and ignites, but after 2-3 seconds the 3A fuse on the board blows.

Fuse blown on gas furnace [ 1 Answers ]

Furnace was blowing out cold air and I found that the pilot needed to be lit. I lit the pilot, now the fuse has blown. I replaced the fuse and it keeps blowing out. What do I need to do?

Fuse in furnace blowing [ 4 Answers ]

My buddy has a payne heat pump system with a payne air handler and every time the heat is turned on at the termostat the fuse blows in the air handler cabinet. The fuse will not blow if emergency heat is turned on or the a/c what is the problem here? I have been working in hvac for six years but...

Comfortmaker Furnace Fan blows in line fuse and will not allow furnace to work [ 1 Answers ]

I have a Comfortmaker Furnace (approximately 1998/99) and the fan will not turn on allow the furnace to heat. When I try to turn the furnace on it blows a 3 amp fuse at the blower motor. I removed the fuse and jumped it and all it will do is make a faint buzzing noise and not turn on. I can...