    Unusual Furnace Cycling
    I have a Goodman GMCE075-3 forced air furnce. This morning I came home from vacation and the house was 59 degrees. The circuit board indicated an open limit switch, however, upon testing the switch it was not open. There are three additional aux limit switches wired in series around the burner enclosure. I manually reset these. Now the furnace runs but periodically the burners will shut off. They will come on perhaps five to ten minutes later. During this time the fan continue to run at high speed as if the burners were operating.

    Question: Can the thermistor comprising the limit switch be out of kilter such that it would not test open but periodically fail depending on temperature?

    What exactly are the auxiliary limit switches testing?

    Thoughts?

    TIA -
    Eric (the homeowner)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 1, 2008, 10:03 AM
    A limit switch can go out of calibration and cause this kind of problem.
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #3

    Feb 1, 2008, 10:12 AM
    The main limit switch controls the heat over the burners by the main heat exchanger, as a safety switch... an over heat condition such as a dirty air filter, bad blower motor, over fired burners, fan speed too low, or feed / return vents blocked or closed will trip this switch to the open position and shut down the unit. ( blower will run to cool off the unit) The aux. limits are located in other areas of the furnace to sense the same high heat conditions, you can test them by checking across both terminals with a volt meter on the connunity setting with the two wires removed ( and power off to the unit) and another test that is performed by HVAC techs is to place a temperature thermistor at that location to check the actual temp vs what is the temp rating of the safety limit... I have seen bad limit switches, which open on a much lower temp that the proper temp to operate at. NOTE: NEVER bypass these safety devices to run your funnace!!
    ebstauffer's Avatar
    ebstauffer Posts: 2, Reputation: 1
    New Member
     
    #4

    Feb 1, 2008, 11:56 AM
    Quote Originally Posted by tsa7man
    NOTE: NEVER bypass these safety devices to run your funnace!!!!!
    I must admit that during the initial panic phase that exact thing did cross my mind. I have had a lot of construction going on in the house. I will check to ensure that all of the vents are open and the filter is clean (I have been replacing it weekly due to sawdust in the air). I do in fact have a thermistor for my fluke multimeter. What plenum temp would I expect to see? Also, for a given limit switch (mine main is the Texas Instruments B13709-10) how might I find the open/close specs?

    Thanks for your answer, by the way!
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #5

    Feb 1, 2008, 02:00 PM
    The specs should be on the limit switch itself. So I would replace it with one with the same specs, if that proves to be the problem.
    Maybe you should check the limit switch for continuity on one of the occasions when the furnace has acted up to see if it is open.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace cycling [ 2 Answers ]

My newer energy efficient furnace cycles every 10 minutes about, I have a new one story home that is very well insulated.

Furnace cycling [ 1 Answers ]

I have a Trane gas furnace w/no standing pilot it's electronic. Anyway when the t-stat calls for heat it will fire up and the shut of within 5 secs. It will do this approx. 4 times before it will eventually lock itself out and the blower will continue to run not ever reaching setpoint. I know...

Furnace off and on cycling [ 1 Answers ]

We had an air bubble in the vacuum system, removed the clamp, blew in the tube, problem solved-thanks for everyone who looked!

Furnace cycling every 2-3min... puzzling! [ 2 Answers ]

I have a 10-12year old 80000 BTU Rheem gas Furnace, and it is cycling every 2-3 min. The fan comes on, the igniter heats up and the gas goes on and burns, and then 2-3 min later it shuts off and 1-2 min after it start the same cycle over again. Now I have checked and cleaned the flame sensor...

Furnace cycling while heating [ 5 Answers ]

I have a Tempstar hvac (heatpump) with a gaspack. It is about 9 years old. I turned the heat on for 1st time this year to discover the problem. I took the cover off to see this happening: I turn the thermostat up and the pilot is one. After a minute of so, the gas turns on and the furnace lights....


View more questions Search