Your error code is telling you that you have a safety limit string open, meaning either the main temperature limit/ safety has opened due to an over temperature condition, or a "roll-out" safety is open, both will shut down the unit... and only the main blower will run to cool down the unit. Now, you also mentioned an "external load on the W terminal of the fan board... this can be caused by a number of issues. One is a high 24 volt draw on the R & W wires that call for heat to the unit through the T'stat. The first check that should be done is... do you really have a good 24 volt transformer in this unit? Then with the power off to the unit, take off all of the wires to the fan board from the T'stat, and put a jumper on R & W.. Power up the unit, it should run, if it does with no error code your problem is in either your T'stat or wiring to it. NOTE: this jumper wire is ONLY for a test. If you don't feel that you can perform these tests, call a HVAC tech for troubleshooting...
|