    Baseboard heaters
    I have some used baseboard heaters I want to install in my basement. 1) They have two wires on the unit itself and four wires on the thermostat, can I assume my power coming in must go to the thermostat first and then to the heater? 2) The four wires on thermostat are labeled L1 & L2 and T1 & T2 , I assume the L wires are for incoming power and T wires go to the heater unit ? 3) How many heaters can I run off one thermostat ? 4) How many heaters can I run off one breaker ( these are 4 and 5 foot baseboard heaters ) ? 5) Is there any advantage to either solid or stranded wire ( copper ) ? This will all be 240 V I phase.

    Any advice is appreciated. Thanks

    S N
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 27, 2008, 07:53 AM
    You are correct with the wiring, to confirm I added a simple wiring diagram to show that.

    A typical heating circuit will be a 20 amp with #12-2 cable with ground, starting at a 20 amp two pole circuit breaker, feed the thermostat and then onto the heater(s) to be controlled by that stat.

    A 20 amp 240 volt heating circuit can handle up to a maximum of 3840 watts of heat. So you can use one heater at 3840 watts, or any multiple amount of heaters that add up to no more that 3840 watts.

    One circuit can feed more than one thermostat, each that only controls one room. So for example, if there are three rooms, each having a 1000 watt heater, totals 3000 watts, these can all fit on one circuit, just need to feed the circuit to three stats, each controlling it's one heater.

    There is no difference in solid or stranded wire. Most cable, Romex, BX, and MC, is typically all solid. Stranded wire is typically used for conduit systems, as solid wire, while still used, is much more difficult to pull than stranded wire.
    crowr's Avatar
    crowr Posts: 1, Reputation: 1
    New Member
     
    #3

    Jan 29, 2008, 02:20 PM
    Quote Originally Posted by tkrussell
    You are correct with the wiring, to confirm I added a simple wiring diagram to show that.

    A typical heating circuit will be a 20 amp with #12-2 cable with ground, starting at a 20 amp two pole circuit breaker, feed the thermostat and then onto the heater(s) to be controlled by that stat.

    A 20 amp 240 volt heating circuit can handle up to a maximum of 3840 watts of heat. so you can use one heater at 3840 watts, or any multiple amount of heaters that add up to no more that 3840 watts.

    I think I found my answer here, but I want to be sure. I just got back from the electrical supply house and I'm thinking the guy gave me the wrong breaker. I just bought 2 5ft 1250 watt baseboards. So a total of 2500 watts. The guy at the supply house gave me a 30 amp 240 volt circuit. Couldn't I run this off a 20 amp?

    And the 2nd question? Is it easier to run the power to the thermostat first then heater 1 then heater 2? That's my planned installation... just wanted to verify. Thanks!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New to baseboard heaters [ 24 Answers ]

Hello; I need a lot of electrical help/advice. I am trying to install an electrical baseboard heater in a basement room (15'X10'). My friend helped me already do the following: Run the conduit and electrical box for thermostat Pull all the wires Mounted the baseboard heater to the wall We...

Baseboard heaters [ 2 Answers ]

I have baseboard heaters (240) I have two hots coming in to the thermostat one black one white marked as hot I have the black wire feed and the thermostat top wire ran to the black wire of the heater I have the white wire from feed to bottom wire of thermostat and the to the white wire of the...

Baseboard heaters [ 11 Answers ]

I am getting ready to put in 4 baseboard heaters 3 of them will be in one room upstairs and the other downstairs. I need help wiring them all. Let me clarify, the 3 baseboard heaters need to be wired together on one breaker and the other will be on its own breaker. Help.

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...

Baseboard heaters [ 12 Answers ]

Hi all.. New to the forum.. Thanks in advance for any help.. I am trying to set up new baseboard heating in my basement.. My questions are to what size breakers to use and if I can put it all on one circuit.. I want to set up 3 rooms: Room 1 - 2 1000 watt heaters Room 2 & 3 - 1 1500 watt...


View more questions Search