    All programed thermostat settings don't work
    I have a Goodman furnace which is controlled by a Honeywell thermostat. Noticed problems during the daily settings especially "Leave" or "Arrive" the temperature settings aren't maintained. Example: Set for 68 degrees and the temperature will be at least 3 degrees lower. Thermostat has been replaced, same issue. Only settings working correctly are "Awake" and "Sleep".

    Larry
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 24, 2008, 10:10 PM
    What is the exact model of thermostat?
    legman69's Avatar
    legman69 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 25, 2008, 08:58 AM
    The new one is RTH6300B - 5-2 day model

    The old one is TH4110D1007 - 5-2 day

    Similar results for both. This wasn't problem initially just lately. Been in this house 2 years.

    Thanks,

    Larry
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 25, 2008, 01:55 PM
    Here is the manual for your thermostat

    http://customer.honeywell.com/techli...0s/69-1717.pdf

    Here is the operator manual.

    http://customer.honeywell.com/techli...0s/69-1723.pdf

    Try to reset the energy star settings in the above manual. (page 16)

    The thermostat is allowed to have up to two degrees slide from setting.
    The thermostat that is built into the thermostat might not be posting the correct temp.
    Could be dead or weak batterys.
    Check over all the low voltage wiring from thermostat to furnace.

    You may have done all the above since you said the old thermostat did the same thing.
    Now taking that into consideration that both thermostats did this you might take into consideration a install problem.

    MAKE sure that the hole for the wires that come through the wall is SEALED TIGHT.

    This causes major problems because air inside the wall can be much colder than the air in the room. This will cause the thermostat to sense the in wall temperature and not the room temperature.

    Now I know this thermostat is not mounted on a exterior wall? If it is move it to a interior wall.

    Always make sure the batterys are installed correctly and are fresh.

    You have a bit if ammo here so see if any of this helps you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat Pump Thermostat settings [ 3 Answers ]

I have had a Heat Pump for a few years now, but I am not happy because it runs a long time ramping up to the day time temp. Am using more power by using a set back thermostat? Should I set it to a closer temp between day and night? I set it at 67 in the day and 62 at night. If it is about 34...

Optimal thermostat settings fro 2- zone heating [ 15 Answers ]

Hi, I live in a 2- story home with 2- zone heating. Bedrooms are on the 2nd floor. During the day we set the 1st floor thermostat to about 66 or 67 degrees. In the evenings the thermostat for the 1st floor is set to 58 degrees as the entire family will be asleep upstairs. (I live in the...

Carrier thermostat settings [ 2 Answers ]

:confused: I have an old original Carrier thermostat that came with this 28 year old house- (square type by long way up/down if you know what I mean),I don`t owned the house just renting, so anyway Carrier thermostat seems to have a mind of it`s own, the furnace heat always shuts down after about...

New Thermostat, doesn't work [ 2 Answers ]

Just bought a Hunter 44110. Not working. Old thermostat ChasRoberts was wired as follows: G=Green C=Blue R=Red Y=Yellow O=White Instructions would have me tie the blue and yellow to the Y on the hunter.

Thermostat settings and heat [ 3 Answers ]

It seems like my heat pump blows nothing but cool air out of the vents. It is below 10 degrees out right now. I have an them. Het setting on the thermostat but when I switch to that setting the air from the vents feels cool or just not very warm. It also seems as if my furnace never shuts off. ...


View more questions Search