Wiring cord for my transfer switch.
Just bought my generator now to hook it up to the transfer switch. The generator came with a 4 prong 220 plug to fit the receptacle on the gen set. The house has a 4 prong receptacle. I bought a plug to match the house receptacle. How do I make sure that I wire the two plugs together that when I plug the gen set into the house it works the way it should.
|
|
 |
Uber Member
|
|
Jan 16, 2008, 02:03 PM
|
|
Black and red each connect to brass terminals, of which there should be two. The white connects to a silver/nickel terminal, and the green connects to the green terminal.
To be sure all will work when needed, use a volt meter to measure 240 volts across the black and red, 120 volts across black to white, red to white, black to green, and red to green.
|
|
 |
Uber Member
|
|
Jan 16, 2008, 02:09 PM
|
|
Don't forget to remove the neutral to ground bond in the generator when using it for the house.
|
|
 |
New Member
|
|
Jan 16, 2008, 03:49 PM
|
|
 Originally Posted by KeepItSimpleStupid
Don't forget to remove the neutral to ground bond in the generator when using it for the house.
Don't want to sound dumd but what do you mean by removeing the neutral to ground bond in the generator when using it for the house. How do you do this.
|
|
 |
New Member
|
|
Jan 16, 2008, 03:51 PM
|
|
 Originally Posted by KeepItSimpleStupid
Don't forget to remove the neutral to ground bond in the generator when using it for the house.
Don't want to sound dumb but what do you mean removeing the neutral to ground bond in the generator when using it for the house. How would you do this.
|
|
 |
Uber Member
|
|
Jan 16, 2008, 04:42 PM
|
|
You Manual should show where this bonding point is.
You say your house has a receptacle?
You should not use suicide cords,(Male prongs on both sides of your cord)To be safe it should be a Male receptacle in the house, Does your transfer switch handle load of whole house? Manual?
|
|
 |
New Member
|
|
Jan 16, 2008, 05:42 PM
|
|
 Originally Posted by Stratmando
You Manual should show where this bonding point is.
You say your house has a recepticle?
You should not use suicide cords,(Male prongs on both sides of your cord)To be safe it should be a Male recepticle in the house, Does your transfer switch handle load of whole house? Manual?
This is a new house and I had the transfer switch added when it was built. There is a sub panel that feeds things like septic pump, freezer, fridge, and some lights and other curcuits. The transfer switch is manual and is feed by a recessed male plug.
|
|
 |
Uber Member
|
|
Jan 16, 2008, 06:12 PM
|
|
At some point in the generator ground is connected to neutral. This connection should be removable. This is the correct way when the generator is acting by itself.
When you connect a generator to the house, the main panel connects the neutral and ground together.
Having two points of zero volts reference causes problems, particularly for the generator. Current can flow in the ground wire from the generator and the main panel. This condition is not good.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Installing A Transfer Switch
[ 3 Answers ]
I have a 30KW 3 phase generator I purchased from government surplus. After repairing the generator it runs fine and I will only be using 2 of the phases. Now my question. I have a new Cutler-Hamer model DT224URK-NPS 200 amp transfer switch which I have mounted above where my service enters my home....
Wiring ceiling fan switch and light switch
[ 1 Answers ]
I had to replace the flywheel on my Hunter ceiling fan and I had to remove the light kit that was attached. After I installed the flywheel, I forgot to mark the wires for re-connection. This is an older model fan. There are five wires coming from the fan motor--brown, blue, white, black and...
Transfer Switch
[ 3 Answers ]
Ok I am looking to add a transfer switch so I can run my generator when the power is out. I have always been told that my transfer switch needs to be rated higher then my generator's output. The problem is my generator has two output rating stated. In other words, a constance rating of 5,550 kw...
Pull cord light switch
[ 1 Answers ]
I pulled the cord from my pull cord light switch. What should I do? Do I have to replace the whole fixture or can I replace the cord?
OHH!! Before I forget the cord is totally pulled out. There is no cord visible. I haven't take the fixture off
Thanks for all the help:confused:
Transfer switch
[ 6 Answers ]
I’ve recently purchased a Guardian 13kw standby generator with a transfer switch and load center panel. I have a couple of questions 1. The transfer panel had a total of 205 amps through 12 various breakers in it, can I replace some of them as long as I don’t go over the original 205 amps and use...
View more questions
Search
|