    carpet1's Avatar
    carpet1 Posts: 13, Reputation: 1
    New Member
     
    #21

    Jan 14, 2008, 07:52 AM
    Thank you. I think there might have been some issues there because when I disconnected the vent from roof connection and blew on it using a blower, nothing happened at first, but later the motor started spinning. Error 31 cleared. However, error 21 came up. I'm convinced I've erroneously described the situation before when trying to explain what I was seeing. Let me tell you what's happening now: Blower comes on, inducer motor runs, and then surface ignitor lights for 3 seconds or so. Burners never come on. Could it be that the gas valve relay is bad or something? What can I check for? The gas line to the furnace is open and the relay knob is set to on. Thanks...
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #22

    Jan 14, 2008, 09:29 AM
    Quote Originally Posted by carpet1
    Thank you. I think there might have been some issues there because when I disconnected the vent from roof connection and blew on it using a blower, nothing happened at first, but later the motor started spinning. Error 31 cleared. However, error 21 came up. I'm convinced i've erroneously described the situation before when trying to explain what I was seeing. Let me tell you what's happening now: Blower comes on, inducer motor runs, and then surface ignitor lights for 3 seconds or so. Burners never come on. Could it be that the gas valve relay is bad or something? What can i check for? The gas line to the furnace is open and the relay knob is set to on. Thanks...
    Hmmm... limits are good, or no ignition would exist. Thermostat-ok-calling for heat as it shoud. Problem appears to be in igniton. Is gas turned on? At house? At appliance? If so, is there 24VAC across the MV and C terminals of the gas valve (or whatever the two pins are marked). If so, is there gas coming through? 24v and no gas tells you gas valve is shot. If gas is coming through,are the burners clear and clean? Is the flash trail across the burner assembly clear for proper ignition? Is the flame sputtering and dying? If so-clean the flame sensor-replace it if you can as it's probably only about 25USD for a new one or less.

    That sounds like quite a bit of work (it's actually not), but that's the trail you'll need to follow to solve this.
    carpet1's Avatar
    carpet1 Posts: 13, Reputation: 1
    New Member
     
    #23

    Jan 15, 2008, 10:09 AM
    Gas is turned on; shares same line as water heater and another furnace. Checked for 24v on the MV and C connections; nothing (checked it before, during, and after inducer motor was running). Checked for 24v on panel on circuit/mother board, where thermostat connects, and good there. Here's something else that's puzzling me; after a couple of attempts to get furnace going, error 31 came back on and inducer motor would not run, then after two or more times, motor would run and error 21 would come on. Anyway, your help is greatly appreciated!
    carpet1's Avatar
    carpet1 Posts: 13, Reputation: 1
    New Member
     
    #24

    Jan 24, 2008, 12:07 PM
    Thank you all for contributing to the resolution of this problem and educating me along the way. The furnace is operational now. The final resolution to the problem was the replacement of the circuit board. I'm not sure how often these go bad, or what caused it, but that solved it. Again, thank you for your assistance...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Anyone know the diagnostic codes for a goodman furnace? [ 3 Answers ]

Hi, I have an older model goodman furnace that powers up the vent fan and proceeds far enough in the sequence for the electric igniter to glow, but then never releases gas to complete ignition. I replaced the gas valve last year, so I am hoping it isn't this again. I am getting an error code on the...

HVAC Diagnostic steps [ 14 Answers ]

I have a 10 yo White and Rogers system in the attic that this year decided not to start. Last year its sister unit in the basement did the same and a new control unit fixed it (but we chalked that up to sitting in water for several years). Now, when heat is called for, the attic draft inducer...

Furnace diagnostic code [ 1 Answers ]

Concord furnace diagnostics : 3 flashes : Pressure switch is open while inducer is on.

Blower runs but won't light [ 1 Answers ]

I have a Goodman furnace installed in 2006. It is an electronic ignition. The problem is that the blower runs but it won't light. Any suggestions.

Magic Diagnostic Machine [ 2 Answers ]

I am curious at what Point the general public started believeing Shops had a Magic Daig machine. I get people all the time I have a coolant leak can you put it on the computer? No we don't have one. Well Firestone Does. Jusy so everyone Knows there is No Magic Diag machine The Technician Has to...


View more questions Search