New Member
|
|
Jan 9, 2008, 10:57 AM
|
|
Need to run a sub panel to my attached garage for woodworking shop.
Hi all!
I am a woodworker and need to install a sub panel in my attached garage. The main is a 200 amp panel and my home was built in 2001. I live in AZ and spoke with the city who said they go by the NEC 2005.
I was thinking of running a 60 amp sub panel as this should more than meet my shop needs for now.
I will be running two or three 120v circuits (one for air compressor, one with multiple outlets for several power tools running one at a time, and one for dust collector to run with power tools on a separate circuit) and one or two 240v circuits (one for band saw, one for table saw, and maybe one open for expansion down the road) from the sub panel and possibly expanding down the road.
1. Is 60 amps enough and are there enough panel openings on a 60 amp panel for this many separate circuits?
2. If I go with a 100 amp sub panel, can I just run a 60 amp breaker in the main and sub panel? (I think the answer to this is yes as I have searched this forum previously? )
3. The BIG one I need clarification on….. what cable should I run to the sub panel? #6 for 60 amp or what for a 100 amp? I have almost 100 feet from the main panel to the location of the proposed sub panel location and am obviously concerned with voltage drop. I’ll be running everything through the attic.
4. Also, do they make larger gauge cables that are “all-in-one” cables or will I need to buy three separate cables and a ground wire?
5. Since my garage is attached, I just want to make sure I don’t need a ground rod on the sub panel. My understanding is that I will connect the two Hot Wires to the Hot Bus Bar and the Neutral to the main Neutral Bus Bar terminal and the separate ground to the Ground Bus Bar??
I’m not an electrician, obviously, but have done a lot of reading on this and just want to make sure this seems correct.
I really appreciate any guidance anyone can give me. Thanks so much.
-Steve :cool:
|
|
 |
Uber Member
|
|
Jan 9, 2008, 03:52 PM
|
|
My answers are in bold:
1. Is 60 amps enough and are there enough panel openings on a 60 amp panel for this many separate circuits?
To size a feeder and a panel, need to know the load of each tool and circuit. The load can be in amps, wattage, or horsepower. I suspect 60 amp is fine, but I cannot speculate without knowing the load.
2. If I go with a 100 amp sub panel, can I just run a 60 amp breaker in the main and sub panel? (I think the answer to this is yes as I have searched this forum previously? )
Yes.
3. The BIG one I need clarification on….. what cable should I run to the sub panel? #6 for 60 amp or what for a 100 amp? I have almost 100 feet from the main panel to the location of the proposed sub panel location and am obviously concerned with voltage drop. I’ll be running everything through the attic.
I would run, if allowed in your area, #2 aluminum, or #4 copper, for either 60 or 100 amp feeder. This will solve the voltage drop issue.
4. Also, do they make larger gauge cables that are “all-in-one” cables or will I need to buy three separate cables and a ground wire?
#2 aluminum is available in a 4 wire cable assembly, called SER cable. Copper cable is available but only from an electrical distributor.
5. Since my garage is attached, I just want to make sure I don’t need a ground rod on the sub panel. My understanding is that I will connect the two Hot Wires to the Hot Bus Bar and the Neutral to the main Neutral Bus Bar terminal and the separate ground to the Ground Bus Bar??
Correct, a ground rod is not needed for a subpanel that is in the same building as the Main panel, only needed for a separate building. Keep the neutral isolated and insulated fro any equipment grounds, do not install the screw that comes with the panel intended for bonding the neutral bar to the metal can.
Since your not an electrician, you will be applying for a permit and inspection from your local building dept?
|
|
 |
New Member
|
|
Jan 9, 2008, 04:17 PM
|
|
Thank you so much for your response, sir.
What a great resource this website is and kind folks like yourself anwering these questions so quickly. I really appreciate it.
And yes, I'll get a permit for the job, but wanted to make sure I was on the right track first. Thanks again.
Steve
|
|
 |
Uber Member
|
|
Jan 9, 2008, 05:41 PM
|
|
Your welcome.
The promptness is purely right place right time.
Certainly does not happen for every question.
Talk this over with your inspector before doing any work or buying material.
Hopefully he will be consultative and give a few tips. But don't take it personal if he is a prick. They are not suppose to offer any advice , at all. But most will tell you if what your planning is correct. Keep in mind, some do not care for homeowners doing their own work, even thou it is allowed by state law.
Can't say I blame them, sometimes.
|
|
 |
Junior Member
|
|
Jan 10, 2008, 06:34 AM
|
|
I live in Phoenix. I installed a sub in my garage/shop. The first thing I wired for was an air conditioner. Believe me... that isn't a luxury around here in the summer. I would plan for that if you plan on doing anything in your shop other than the hours of 3:00 a.m. to 9:00 a.m. At least the temp in the garage will be down to about 100 degrees during those hours...
|
|
 |
New Member
|
|
Jan 10, 2008, 07:51 AM
|
|
Thanks for the response, Cobraguy.
I've spent the last couple of summers out there in the heat and can definatley appreciate the idea of AC in the shop. I'm leaning toward the 100 amp sub panel so I can expand down the road and maybe treat myself to some AC in the summertime!! (Or I can just come over and work in your shop!! :) Just kidding, but thanks for the input.
-Steve
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Wiring 100amp subpanel in attached garage
[ 3 Answers ]
I would like to wire a 100amp subpanel located in an attached garage. I plan to use a 100amp breaker on the main panel for the supply. The wire will run though the attic ~30ft. I plan to run #4 copper in conduit unless recommended otherwise. I would appreciate any suggestions. Thanks. J
Grounds to be used for shop sub panel
[ 4 Answers ]
Have metal pole building about 80 feet from house. I intend to run 100 amp from house panel to sub panel in shop. Originally purchased a cutler hammer mail lug panel CH8L125SP for this use (on sale) but think I would rather have a 100 amp main breaker panel so as to use as single disconnect in...
Attached garage not insulated
[ 9 Answers ]
I've got a ranch house with an attached garage. The garage is not in any way insulated which doesn't really bother me. What does bother me is there is no wall in the attic between the house and garage. I live in upstate NY and the winters are pretty cold up here, should I build an insulating...
Installing a 60 AMP sub panel for a work shop
[ 1 Answers ]
I have a 200 AMP main panel for my residence with all the breaker slots filled. I plan on removing 2 20 amp breakers and installing a 1 60 x 2 20 amp consolidated breaker in to the panel. Well at least I am told I can do this. I plan on having 2 240 VAC 30 amp breakers in the shop (one will have...