    Reversing valve
    Trying to start up a water to air heat pump. The high side r-22 kicks out at 400psi within 3 seconds whether in cooling mode or heating mode. The reversing valve (alco 401RD-10F57) clicks but seems to be the only obstruction that would prevent refrig. Flow. There seems to be no suction side change. This unit has been sitting new/unused/charged for 10 years prior to installing (as a replacement to an identical unit)
    Thank you for any suggestions or insights.
    Tkornylak
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 7, 2008, 10:41 PM
    Check to see if it has a liquid side pump down selonoid valve on it. If it does it has to be energised for the refrigerant to flow. Could also be a dead TXV power head.
    tkornylak's Avatar
    tkornylak Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 8, 2008, 06:20 AM
    Thank you. There are no pumpdown selonoids. What are the possible tests for the TVX and is it repairable?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 8, 2008, 07:48 AM
    Disconnect sensor bulb and hold in hand to heat up. The refrigerant should flow. If not then the TXV is defective.

    Have you checked the suction and discharge valves to make sure they are open?(sounds funny but I have seen that before on a replacement)
    Could the unit be overcharged?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Reversing Entries [ 7 Answers ]

I know reversing entries are used to keep from confusing and over/under estimating a certain account in the next period, but here's my question. Are reversing entries really necessary in your accounting period?; even though they are meant for reminders there are other ways of doing that without...

Jantirol heatpump reversing valve hums constantly [ 2 Answers ]

My jantirol heat pump when the thermostat is in the off position the reversing valve in the heat pump hums and is hot. If I turn the breaker off in the handler space then it stops. That circuit breaker is the only thing that stops it. The cutoff next to the heat pump will not stop the hum and...

Reversing valve or Compressor? [ 1 Answers ]

Stuck on this: Unit has equal pressures when it starts up... compressor does not sweat even from common suction... the reversing valve selenoid clicks but does not switch... I know pressures along with 24v switch the reversing valve... but it seems valves are bad in compressor? Any help would be...

Reversing entries [ 2 Answers ]

I have a problem that says to reversing entries by the previous year's adjusting entries. It want me to reverse Interest income $307.50 Salaries expense That give me Sales salaries $1306, Office Salaries $607 I will add them together and get $1913 for Salaries payable. Interest Expense $1,755. How...


View more questions Search