    New Tappan Furnace overheats & shuts down
    Tappan Furnace Problem


    Last season I had a Tappan furnace installed in my shore home.. during the winter I set the temp at 55 when I'm not there & when I come down I set it at 70... the furnace kicks off around 62 & I need to reset the system. The contractor has replaced the reset buttons & installed a kit which was supposed to solve the problem... no luck yet... Tappan has yet to admit that there is a problem (it's been going on for 10 months)... the contractor has about 5 other units with the same problem... is there a solution or should I demand another unit? Defective furnace or installation problem
    Augie T
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #2

    Jan 2, 2008, 08:34 AM
    If the system is shutting down due to too high of internal temperatures, your duct system could be either too small or restricted. If hot air cannot leave the furnace quick enough, the internal safety could cause it to shut off. Question, after the house has achieved a temperature, does the system stay on? If you go from 55 to 70 degrees you are asking a lot from the system. Test your return air ducts by removing the blower door and tape the door safety switch in the down position. With the blower operating, does the furnace suck the blower door closed? If it rips it from your hands, you just discovered that there is not enough return air coming back to the furnace. If it just pulls lightly against your grip, the air flow is good but you may not have enough hot air registers to get all that hot air out of the furnace.

    As the system is running and the blower door back in place, check te temperature of the ductwork. One duct should be warm to the touch and the other cool. If you cannot hold your hand on the duct because it is way too hot, you again have an airflow issue. You may be able to increase the blower speed to compensate for it however the real issue here is duct size.

    You could try a programmable thermostat that allows you to call into your seasonal home and slowly increase the temperature to compensate for the large demand for heat when you first arrive, or just bite the bullet and get your ducts in a row!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace overheats-limit switch kicks in [ 6 Answers ]

I have a Bryant model 376C, induced combustion, gas fired, downflow/horizontal furnace with an overheating problem. Unit is approx 18 yrs old. Limit switch blew, replaced it, and replaced dirty filters and slightly increased blower motor speed. New limit switch also kicks in. Air/return...

Furnace shuts down generator [ 15 Answers ]

I have installed a 16kW standby generator and I am having a problem with the furnace. It is a 10kW furnace and the rest of the generatoris running lights, outlets and a well pump. When the generator starts, everything is fine. Then about five minutes with the generator running, it trips the 65 Amp...

Furnace shuts down early [ 1 Answers ]

I have a "Day & Night" gas heating/air 5 ton unit. When I turn on the heat in the morning all works fine but the unit shuts down before the desired temp. It's not the thermostat because I know enough to go out to the unit and bypass the thermostat. Nothing happens. After an hour or so, the unit...

Furnace shuts off [ 2 Answers ]

My oil furnace will shut off during the day or evening. I can usually get it going again by pressing the restart button. Even then, sometimes it won't click in, sometimes it will run for half a minute and shut down. If I restart a few times with very short runs, it evventually will run for an hour...

Comfortmaker furnace shuts down [ 1 Answers ]

I have a comfortmaker furnace that is vented with a 3" duct and a blower. Recently it started where the furnace will run through it's course , the glow plug will work, then the gas valve opens and you can see the heat in the exchange and then after a few minutes the blower will come on and heat...


View more questions Search