    I have a 70,000 BTU boiler with currently 3 of 4 zones used.
    2 are for heat and 1 is for the hot water coil (the priority zone)

    I recently added 2 more zones from an addition I have done. They have kickspace heaters and the FL100 in the floor heaters from Smith Environmental. (I describe them as a radiator in the floor with a blower)

    I have done all the plumbing to the boiler but not the hook up yet. I keep looking at the zone controller and wondering how to update it to add more zones.

    Any advice on changing it and what I may be getting into is very appreciated.

    Mike
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 2, 2008, 07:41 AM
    Combine both the new zones into onethermostat and one valve for both. This will give you the maximum you can control with your setup you have now.

    Option B is that you get a larger zone control and wire/valve/thermostat each separate.
    mike08201's Avatar
    mike08201 Posts: 32, Reputation: 1
    Junior Member
     
    #3

    Jan 2, 2008, 04:19 PM
    I want to add zones. That's why I ran it that way, or I would have saved $200 running one set of pipes instead of 2 LOL

    Just don't know what I'm getting into with the zone box. I would prefer some advice/tips ahead of time if its possble
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 2, 2008, 04:41 PM
    You are really getting into nothing but low voltage wiring. A zone control come with a wiring diagram and if you can follow one of those your good to go. Just get a control that will service all your zones you have now or get the next size up if you plan on another addition.
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #5

    Jan 2, 2008, 05:03 PM
    I would use the remaining spot on your existing zone control and then purchase a single zone control (the same brand as the existing one) for the last zone. Tie the "T" contacts from one control to the other so the boiler will turn on. Controllers are much more service friendly than a rat's nest of wire at 3 AM.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Evaporative Emission Control System Purge Control Valve circuit Malfunction [ 3 Answers ]

p0443 Evaporative Emission Control System Purge Control Valve circuit Malfunction on mazda melinia s 1996 83k?what is the next stip? I cleared the check engine light and it went off ,and after 60miles driving it cames back again?why and how can I fix it ? Also what is the cheapest way to reset...

Changing the valve in a Price Pfister single knob shower control [ 1 Answers ]

I was trying to replace a leaky valve in a price Pfister shower control knob but can't figure out how to remove the old valve. Is there a special tool for this? Thanks

Zone control adjustment [ 1 Answers ]

I just bought my house in May and now that its cooling off, I have started using the gas heat. I discovered a damper system was installed at some point and its shutting off any warm air to the upstairs. I need to either adjust the damper or just turn off the system with all dampers open. Any...

Changing the outside unit vs. Changing the whole system [ 7 Answers ]

My outside unit leaks Freon and needs to be replaced. The system is about 9-10 years old. Initially, the contractor gave me a $2500 estimate to change the outside unit to a new Trane XR14. When the written estimate came, it included changing the coil and fan package inside (it's a ceiling unit)...

Dual Zone Control for Whole House A/C [ 4 Answers ]

Dual Zone Control for Whole House A/C I have a 5 TON Unit (Carrier) and a WHITE RODGERS 1F90-371 Programmable Thermostat in a 5/4 Private Dwelling. I've started using a closet for all my I.T. Gear, Servers, Raids, WiFi Routers etc... as you might guess; the I.T. Closet's become a hot-box. I'm...


View more questions Search